I would like to know if there are a maximum velocity in sprinklers systems piping per FM and NFPA.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Maximun water velocity in pipes as FM and NFPA
|
RE: Maximun water velocity in pipes as FM and NFPA
http://www.sprinklernet.org/technical/articles/watervelocity.html
As far as FM, I think they have also removed the velocity requirements. They used to mandate 32 fps in "tree mains", and 20 fps in gridded branch lines. However, I have not had problems in the last 5 years or so when I have exceeded those values.