Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...This is easily the most helpful website I've ever used, and this is the best forum with the quickest response time bar none...."

Geography

Where in the world do Eng-Tips members come from?
TTheHammer (Mechanical)
30 Mar 04 10:03
Hi All,
I guess this will be abit long, I'm designing the controls for a regulating station for a Class I Div I location, and all of the inside instrumentation are exiting via a terminal block then going to the control building. my question is :

Can I connect also the field equipment (which is outside the Class I Div I area) to the same terminal block, then pull everything through one conduit to the control building?

Or you think that I should have a seperate conduit for field equipments?

Thanks Guys
hacksaw (Mechanical)
31 Mar 04 8:34


it depends on the area class for the terminal blocks.


TTheHammer (Mechanical)
31 Mar 04 8:45
Thanks Hacksaw, I guess the TB are in Class I Div II, (I mean outside the building.
Helpful Member!  ilan7 (Mechanical)
3 Apr 04 11:26
Do not see any problem with using one terminal strip.  PLease note:
1.  If you are using Intrinsically Safe equipment at the Zone 1 area,  you must have separate cables, boxes and terminals for them.

2.    You just have to seal ALL the CABLE entering the Classified area  at one end to avoid any posible gas flow inside the cables into the Non-Hazardous areas.
ICman (Industrial)
30 Apr 04 10:46
I strongly suggest you find an engineer with experience in hazardous area applications to review your system. I was just involved with a similar case, and was somewhat surprised with the unfamiliarity most had regarding hazardous areas. Guess I've been too close to it .

You may or may not be able to use a terminal strip for various devices. For instance, you cannot combine AC- and DC-powered equipment on the same terminal strip. The terminals must be appropriate for the area, as well.

ilan7 is correct in his recommendation that you seal the conduit. Intrinsically-safe devices are treated differently than other systems (like those rated for the area, or the use of explosion-proof enclosures), and the whole system must be designed correctly.

This is important! You need to be sure your system is safe, and will not pose a hazard to the public or to company personnel. Have the installation at least reviewed by a professional.
SEB54 (Petroleum)
11 May 04 9:43
Maybe you could use pneumatic purge system without eletrical supply...son you don't have to treat current

bye

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close