LOAD FLOW STUDY
LOAD FLOW STUDY
I WOULD LIKE TO KNOW ABOUT POWER LOAD FLOW ANALYSIS
6 0R 7 220 KV BUS SYSTEM
1) GUIDE LINE HOW TO START IT
2) METHDOLOGY STEP BY SETP
3) ANY FREE SOFTWERE SITE
3) WHICH PARAMETERS REQUIRED.
4) voltage drop analysis
RE: LOAD FLOW STUDY
RE: LOAD FLOW STUDY
I highly recommend that you look at IEEE Std 399 - Power Systems Analysis; This standard will give you the methodology for performing a load flow/voltage drop study. There is a chapter devoted to load flow studies along with examples. This is an excellent reference to review before conducting any electrical engineering analysis/calculation
Response for #4, #5 =
Another standard you should look at is IEEE Std 141 - Recommended Practice for Elec Power Distribution; This standard has a chapter on voltage considerations (Chap 3).
Response for #4 =
The type of data that you need to perform the study:
a) equipment ratings (power, voltage, etc.)
b) impedances for all components (motors, cables, buses, etc., including cable and interconnecting bus lengths)
c)voltage profiles for source (e.g. utility normal operating range, what is lowest expected?)
Remember that you should add positive manufacturing tolerances to all impedances (if in the design stage, as per applicable standard(s)) to maximize voltage drops across all components in order to obtain worst case results.
Good luck!
RE: LOAD FLOW STUDY
RE: LOAD FLOW STUDY
E.g. SKM, Inc. (DAPPER, A-FAULT, etc.), OTI, Inc. (ETAP), EDSA, etc.
These businesses have their web sites.
http://www.skm.com
http://www.etap.com
http://www.edsa.com
for more info