star/delta o/load

star/delta o/load

star/delta o/load

(OP)
i have a 3 phase motor  pump rated at 17.9A full load do i fit an o/load in the main contactor line and set it at 11A this being 17.9/sqrt3

RE: star/delta o/load

Yes, if this is a standard Y/D starter with O/L relay on the load side (in series with motor windings), of the main contactor.  In other words if the O/L relay is seeing the phase currents of the delta conection then your statement is true.

RE: star/delta o/load

Regularly on wye-delta starters the full load current of the motor is shared between two contactors ( 1M and 2M), then the thermal units must be sized for 58% of the full load ampere rating of the motor .

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources