Cable glands and single core cables
IEC 60079-14 requires that for cables directly entering an enclosure greater than 2 liters and with a source of ignition need to be sealed in some manner.  Section 10.4.2 allows compound sealed cable glands.
My question is, is a compound sealed gland required for a single core cable?  Seems to me a non-compound gland should be fine, as allowed by the words "other equivalent sealing arrangements".  The compound serves no purpose with a single core cable.
Any comments?  Or better, relevant experience?
RE: Cable glands and single core cables
If cable is from source of ignition, then seal glands shall be required.
INSTRUMEN:
Do you have a reference for this statement?  The word "shall" indicates that you do.
TMD