fan selection
fan selection
fan selection
<dear all,
  i hava an industrial hall with 45,000 meter cube volume which must be kept 4 degree c above the ambient which is 40 degree C as design temperature, i have come up with fan size of 160,000 meter cube/hour please somebody check it and let me know what will be the power consumption of such huge fan?
RE: fan selection
We can provide you some pointers so that you can check this on your own(as per the site policies).
Fan BHP = Air Flow (in cfm) x DP across fan (in inches WC)/(6356 x eff. of fan)
Fan kW = Air Flow (in Cu.M/Sec) x Dp across fan (in kPa)/eff. of fan
Include transmission(100% for direct coupled fans) and motor efficiency to get motor power rating.
Eng-Tips.com : Solving your problems before you get them.
RE: fan selection
What if you just used heaters instead? Hopefully no people have to work in there.
RE: fan selection
The outside air you bring in will see the following loads:
- heat from the fan
- heat from the lights
- heat from solar loads through glass
- heat from transmission through walls & roofs
- heat from people inside
- heat from equipment inside
You need to list Btu/hr loads from each.
 then calculate CFM = (total Btu/hr loads) / (1.1 x Td °F)
You have to do a trial & error for the fan heat so the fan bhp will match the fan size required to provide the required CFM.
Fan bhp = (CFM x TP in. wg) / (6344 x Eff)
Where TP = in. wg fan total pressure
Eff = decimal efficiency you can use 0.65 as a good approximation
Fan heat in Btu/hr = Fan bhp x 2545