I am desingning an underground HDPE fire fighting water net.
¿Does the HDPE pipe must be UL approved ?
Regards,
Split
¿Does the HDPE pipe must be UL approved ?
Regards,
Split
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: NFPA-&HDPE underground
YES! Look at www.pip.org PIP PN12PD0H01
Piping Material Specification 12PD0H01
FM Class 150, High Density Polyethylene (HDPE)
Fire Water (UL/FM Approved) (Underground)
PIpie:FM Class 150 HDPE (PE3408) ASTM D3350 - CL 345434C, FM
Leonard@thill.biz
www.thill.biz
RE: NFPA-&HDPE underground
Addtional information:
DESIGN CODE: NFPA 24
Leonard@thill.biz
www.thill.biz
RE: NFPA-&HDPE underground
Do you have an apporved Piping Classification Specification.
Are going to use the above PIP.ORG Piping Classification Specification: Pipe, fittings, Valves, flanges, GASKETS,
BOLTING.
Leonard@thill.biz
www.thill.biz
RE: NFPA-&HDPE underground
RE: NFPA-&HDPE underground
1) What is the code of construction that you are building this to? Is this code a legal requirement, or has it been adopted as good engineering practice for the system that you are designing?
2) What jurisdictional requirements are in place? Is there a fire code that you are required to be in compliance with? If so, does the fire code reference different codes of construction, or NFPA documents as mandatory requirements?
3) In the case of a firewater system, the insurance industry often plays a big role. Do the insurer's of the plant require that UL/FM approved piping and components be used for fire protection systems?
Blatantly pulling specifications of the internet, and using them without questioning if they are applicable to your particular situation is a dangerous practice. We routinely waive the requirement for UL/FM approved components where we can show that it is not required. Additionally, as you begin to design larger diameter systems, you may find that all of the components may not be commercially available, and specifying UL listed components could end up costing you a lot of money...
Hope this helps.