Looking for a code or CSA Standard for reasons why metering PT's must be in an enclosure when used in a disconnect switch
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
CSA or CEC Code Ruling for PT's
|
RE: CSA or CEC Code Ruling for PT's
[From below the 49th] for metering, is it possible the enclosure is meant to be sealable to limit access to revenue-measurement components?
RE: CSA or CEC Code Ruling for PT's
6-402(1) Meter loops shall be installed so that: (a) Conductors between the service box and the meter are inaccessible to unauthorized persons;
and
6-404 (1) Instrument transformers used in conjunction with meters shall be installed in metal enclosures, except where access is only to authorized persons.
Just trying to keep people from modifying the wiring I guess.