Electro-mechanical resonance frequency
Has anyone got information on Electro-mechanical resonance? I have seen some info about this with servo motors but this concerns a standard AC induction motor. I think that if this resonant frequency coincided with VFD firing frequency or a integer multiple it could cause severe torsional vibration. What do you think? Does anyone check for this potential problem?
RE: Electro-mechanical resonance frequency
Electromechanical Resonance
Roubicek, O.
Dept. of Electr. Syst., Res. Inst. of Electr. Eng., Praha 9-Bechovice;
This paper appears in: Electric Power Applications, IEE Proceedings B [see also IEE Proceedings-Electric Power Applications]
Publication Date: Jul 1990
On page(s): 281-292
Volume: 137, Issue: 4
ISSN: 0143-7038
References Cited: 24
CODEN: IPPADZ
Abstract:
The symmetric double acting oscillating synchronous linear motor with longitudinal functional air gaps is very well suited to the system synthesis of the electronically controlled drive for working resonant machines used in industrial vibrational techniques. It can be designed for a stroke of up to a few centimetres and a working frequency ranging from about 6 to 70 Hz. What is important in practice is the motor operation in electromechanical resonance with a compensated synchronising (AC) motor circuit and a compensated mechanical load. Then, the operational motor characteristics, derived under the assumption of harmonic oscillations, are functions of real variables. An analysis of these characteristics yields the features of a steady-state motor with harmonic oscillations. Attention is paid to the motor self regulation and the control of the velocity or path amplitude of its oscillations. The theoretical outcome, applicable also for the case of a not fully harmonic motor power supply from a static convertor, is in good agreement with the experimental results obtained from researching motor prototypes of 1 and 5.7 kW
The excitation can be electrical (torque pulses, lateral magnetic force variation) or mechanical. If either type of excitation corresponds to mechanical resonance frequency, there can be trouble.
With regard to torsional resonance, it is most often excited by impacting-type torque pulses from the load (such as reciprocating compressor). If torque pulse rate is an integer subharmonic of torsional resonant frequency, there can be problems.
Induction motors I think are less susceptible than sync motors because the low-resistance squirrel cage provides very heavy damping action for instantaneous deviation from steady state speed.
I think torsional analysis is not done by many users except for larger trains of equipment. OEM's may do it for smaller pieces of equipment.
http://www.engdyn.com/papers/papers_torsional.htm
At this link you will find a nunmber of papers on torsional analysis and most are available free on-line pdf (others are available for phone call.
For example, click on "Torsional Analysis of VFDs" and then look for the pdf icon near top right-hand corner of the page (2.3 Megabytes).
http://www.mic.dtu.dk/research/bioprobes/Publications/Abadal-Electromechanical%20model%20of%20a%20resonating%20nano-can-based%20sensor%20for%20mass%20detection.pdf
for Equation 5
http://www.mtf.stuba.sk/veda/casopis/2004/cislo1/mudrik/mudrik.pdf
etc. There is a lot of it on Web
Is there any special relevance between torsional resonance of vfd and your paper: "Electromechanical model of a resonating nano-cantilever-based sensor for high-resolution and high-sensitivity mass detection"
I think it is safe to assume that anyone who can make it to this site knows how to use google. So spewing random google links with no relevance to the question does not help, in fact wastes people's time following unrelated links under the assumption that if someone posts them here they have some relevance.
If you are going to post links, may I suggest you limit it to links that you personally have determined have some relevance to the question.
At an instant in time, in the stator of a 4-pole motor there are 2 North poles and 2 South poles right? Simultaneously, on the rotor there are also 2 Norths and 2 Souths. We all know how they got there so we'll skip that part. The magnetic fields interact to pull the rotor around. This pull is the spring in my resonant system. The mass is of course the rotor.
So I'm looking at a torsional resonance in the motor itself. I expect this to be a high frequency, but what if its not. Or what if, I now use this motor with a VFD that may have many harmonics of line frequency? Does anyone check for this at design stage?
From my way of thinking, the resonance is mechancial. It can be lateral or torsional.
///Please, revisit my posted links for the idea of mathematical model of electromechanical system.
Specifically, Equation 5
V (x) = sqrt[0.533E W^3 x^3 (s-x)/[e l^4 (x-(s-x)ln|s/(s-x))|]] (V(m)) (5)
e is medium permittivity
Clearly, it can be seen that there is a mixture of electrical and mechanical variables.
This is consistent with my statement ""It just depends how the electromechanical equations, possibly differential equations are setup.""
Then, comes more difficult part, namely how to form the mathematical model to obtain the sought results about the torsional vibration/resonance.\\\
///It is not quite explicit in the posted link which reference is covering electromechanical modeling that would include electromechanical resonance.
electricpete,
Is there any special relevance between electromechanical resonance of vfd and your papers dealing with torsional resonance?
If you are going to post links, may I suggest you limit it to links that you personally have determined have some relevance to the question. \\\
The low stiffness often leads to serious problem with tuning of servo system especially depended by ratio of load-to-motor moments of inertia (mismatch ratio).
More details you may find from Tutorial and paper of George Ellis (Kollmorgen) and Richard H.Welch Jr.(Welch Enterprise).
jb - your comment on possible electrical interaction in the resonance is accepted. Regarding relevance of links, I would suggest rather than making a ridiculous argument that your link is relevant and mine is not, you just accept my comment as a constructive suggestion and refrain from repeatedly posting links direct from google without any consideration of relevance.
///Rather than claiming that your postings are relevant and others irrelevant, it would be better that you point out where the electro-mechanical resonance is actually appearing in your postings to satisfy the original posting request. I just feel sorry for criticizing others while delivering very little or nothing to the original posting.\\\
We have come to expect it from you. Apology accepted.
There is a rambling long-winded discussion that I participated in at
http://www.vtab.se/PHP-NBoard/html/images/materiali/Forum2/HTML/001884.html
(note there are 2 pages of it... click on button near bottom of 1st page to get to 2nd page).
From my perspective, the induction motor field acts not like a spring, but like a damper. Torque is proportional to slip. I think if you build a math model on this including linearization about the steady state point, you will conclude the function of the torque produced by induction motor is equivalent to a damping element, not a spring. As such it does not introduce any new resonant frequency into the system. I may be mistaken and I welcome someone to explain why an induction motor field should act like a spring.
http://www.reliability-magazine.com/ubb2000/ubb/Forum2/HTML/001884-2.html
define w(t) = radian speed of rotor
define w0 = steady state speed
define w1(t) = deviation from steady state speed w1(t) = w(t) – w0.
theta(t) = position as function of t
theta0(t) = w0*t = steady state position - revolves steadily as function of time
theta1(t) = deviation from steady state position = theta(t) –theta0
define Tmot = motor torque
define T0 = steady state motor torque
define T1(t) = deviation from steady state motor torque = Tmot-T0
define Tload = load torque
define Ttotal = total torque = Tmot+Tload
define wsync – syncrounous speed
k = proportionality constant between slip speed (wsync-w) and torque
Tmot = k*(wsync – w(t))
substitute in for w(t)
Tmot = k* (wsync – w0 – w1(t) )
Tmot = k*(wsync-w0) – k*w1(t)
recgognize k*(wsync-w0) = T0
Tmot = T0 – k*w1(t)
Ttotal = Tmot +Tload
Asssume Tload constant at steady state value Tload = –T0
Ttotal = Tmot – T0
substitute for Tmot
Ttotal = T0 – k*w1(t) – T0 = -k*w1(t)
Ttotal = -k*w1(t) looks very much like damping equation Fdamp = -c * dx/dt = -c*v
F=ma type relationship is
Ttotal = J*d^2/dt^2 ( theta(t))
substitute in for theta(t)
Ttotal= J*[d^2/dt^2(theta1(t)+ theta0(t)]
But theta0(t) = w0*t, so d^2/dt^2(theta0(t)) = 0
Ttotal= J*d^2/dt^2(theta1(t)]
substitute in for Ttotal
-k*w1(t) = J*d^2/dt^2(theta1(t)]
substitute w1(t) = diff(theta1(t))
-k*diff(theta1(t)) = J*d^2/dt^2(theta1(t)]
This can be recognized as a damped system.
The response to a perturbation in theta is theta(t) = theta0 * exp(-k/J).
=> induction motor torque coefficient k plays the role of damping.
* Note - if you have a syncrhonous motor then the field will introduce a spring which add a resonance to the system.
The response to a perturbation in theta is theta(t) = theta_initial * exp(-k*t/J).
(I don't want to re-use the symbol theta0)
The response to a perturbation in theta is theta1(t) = theta_initial * exp(-k*t/J)
Don't your equations assume there is only one spring to begin with? Where is the term for the force which accounts for nonlinear response in magnetic force due to varying the distance between poles in the rotor and stator? I do agree that the effects of resistance and inductance in the electrical circuit work to keep the vibration amplitude from going to infinity.
In the analagous mechanical system, the material which is selected for the spring not only determines the spring constant, it also determines a certain damping. As an extreme comparison, if I use a metal spring vs. a rubber one. So it is possible that the electromagnetic forces are not only dampening but storing energy.
Consider that large syncronous machines have shorted-turn windings installed soley for the purpose of dampening low-frequency oscillations. These windings are roughly equivalent to squirrel cage windings.
If there were a force representing a spring created by the electrical field, it would show up somewhere as a term torque ~ k1* theta. But induction motor is symmetric and one position of thete means no different than another. The torque does not care about position of theta, it cares about relative motion w. How can this represent a spring?
The link is here:
http://www.brazosport.edu/~pschimpf/forums/engtips/TwoMassSpringInductionSimpleRev1.PDF
It solves a system of motor rotor inertia, compressor rotor inertia, coupling spring, coupling damping, and induction motor field which acts as dampener. The exciting force is assumed to come from the load end. The variable Xd (d for differential) is examined which presents differential position between motor rotor and compressor rotor i.e. torsional flexing of the coupling.
There is one root at zero frequency (I provide some discussion of interpretation with respect to response to step change in load at the end). This zero frequency root I associate with the motor field. There is one resonance at w=14 which is very close to that computed from compressor mass and coupling spring. The frequency of this resonance may be altered some by the damping effect of the motor field. imho, there is no new resonance created by the motor field because there is no spring action associated with the motor field.
1 - If we were discussing a sync motor, there would be a spring corresponding to the field and an associated resonance frequency. Not so for induction motor.
2 - In a vfd there may be harmonic torques which will serve as excitation. The resonance excited by those torques (for induction motor) would be mechanical.
http://www.ipst.org/TechPapers/2001/IPST01Paper240.pdf
For "Perceptions about new kinds of subsynchronous resonances":
The numerical calculation of different types of drives brought an important insight: also in systems with induction machines an electromechanical resonance can occur, especially during running up. Consequently the torque in the connection components between motor and main engine can reach values much bigger than the maximum stationary breakdown torque (see fig. 8). This highly depends on the mechanical-geometrical and the electromechanical attributes of the entire system. Also the inner mechanical damping has to be considered. As a result, no global predictions about the endangerment of a drive system can be made and must not be made.
In the article I references Engineering Dynamics Paper “Torsional Analysis of VFD’s”, this oscillation is not discussed under system stiffness on pages 2 & 3. It is discussed on page 7, more in context of a driving excitation. Whether or not you choose to call this an electromechanical resonance is a matter of terminology. I can see support for both viewpoints, and I previously have accepted the comment that electromechanical resonances are present.
One logical question is why does the model I showed above not predict this behavior. The model I showed is based on torque proportional to slip. We know this is true at steady state when speed is within a few percent of syncronous speed. It is reasonable to expect it to be approximately true for small transients from steady state condition. It is not reasonable to expect it to hold for faster transients or starting from zero speed. Below breakdown torque, the torque vs slip curve no longer resembles a proportional relationship and the torque no longer represents a damping effect.
Epete,
Please explain why you say this phenomenon only exists in synchonous machines. It may be my misunderstanding of how they work. I will go do some study. Don't VFD's have the potential to make torque pulses? Isn't the ouput wave actually made up of lots of square waves?
The article linked above by jbarots discussing oscillating torque during startup of an induction motor.
///Yes. Beside that, the paper also addresses:
1.
II. USUAL SSR PHENOMENA
The usual SSR phenomena caused by compensated transmission lines can be manifested in three forms: Induction generator effect (IGE), torsional interaction (TI) and torque amplification (TA). These phenomena may occur isolated or simultaneously, and when they occur they can cause damaging oscillations. Hazardous levels might be reached within 0.1 seconds.
2.
For calculation of the electrical resonance, the structure of the electrical system according to fig. 1 can be represented by a reduced model. The resonance frequencies depend on the short circuit capacity of the main system (fig. 4). For the analysis of SSR it is necessary to evaluate electrical frequencies close to:
for the steam turbine: fn - fm= 50 Hz - 18 Hz = 32 Hz
for the gas turbine: fn - fm = 50 Hz - 12 Hz = 38 Hz
where fn is the electrical frequency and fm is the mechanical resonance frequency.
3.
etc.
However, the generators are often considered for the subsynchronous (subharmonic) resonances, since the transmission lines are not directly connected to large induction motors. The impact of subharmonics would be somewhat similar to the detrimental impact on the generator rotors.\\\
jb - I have never heard any reference to induction machine torsional failure associated with power system interaction as you describe. What you describe is associated with syncronous machines.
///Yes, that is possible since, as I mentioned in my previous posting, the transmission lines are not directly connected to large induction motors. The impact of subharmonics would be somewhat similar to the detrimental impact on the generator rotors.\\\