I am looking for assistance in calculating the 300V Zone of Influence with respect to communications equipment protection at a substation. Does anyone have any references on this?






RE: Substation Zone Of Influence
RE: Substation Zone Of Influence
One reference is IEEE standard 367 Recommended Practice for Determining the Electric Power Station Ground Potential Rise and Induced Voltage From a Power Fault
TOC at
http://standards.ieee.org/reading/ieee/std_public/description/psystcomm/367-1996_desc.html
RE: Substation Zone Of Influence
RE: Substation Zone Of Influence
pintalo—
Unfortunately, IEEE does not provide much of anything for free these days, but PDF availability does simplify things a bit.
RE: Substation Zone Of Influence
http://standards.ieee.org/reading/ieee/std_public/description/psystcomm/487-2000_desc.html
for: IEEE Std 487-2000 IEEE Std 487-2000 IEEE Recommended Practice for the Protection of Wire-Line Communication Facilities Serving Electric Supply Locations - Description
RE: Substation Zone Of Influence
http://gpr-expert.com/wire-line.htm
since it addresses in:
Figure 2: Block diagram for HVI installation,
the 300 Volts Point Zone of Influence
RE: Substation Zone Of Influence
Significant induce voltage could be created on control and low voltage power cable by surge during switching, lightning or fault conditions in a substation.
Fiber optic could be an option for control system since is naturally immune to induce voltage.
The enclose article could be helpful for your application.
http://pm.geindustrial.com/faq/Documents/General/GER-3205.pdf
RE: Substation Zone Of Influence
RE: Substation Zone Of Influence
I don't have access to IEEE Std 487 or 367, but wouldn't a calculation of equipotential lines around a facility during a fault give you the 300 volt zone of influence. Several grounding packages (for instance SES CDEGS) allow modelling of the ground system and calculation of earth potential at various points.