Masonry facing
Masonry facing
(OP)
Masonry facing per 2307 at L/600, no support by wood members, 1/2" offset from light-frame face req'd. Std Wt Brick used.
Brick facing to be running bond. Have 16' garage door header, 3.5' pier width each side of opening & 10' of gable at center span. Calcs out for A36 9x4x5/8" Angle, however, this does not appear to be representative of witnessed practice. Do arch mechanics apply to running bond brick faces? Any comments or references welcome.
Brick facing to be running bond. Have 16' garage door header, 3.5' pier width each side of opening & 10' of gable at center span. Calcs out for A36 9x4x5/8" Angle, however, this does not appear to be representative of witnessed practice. Do arch mechanics apply to running bond brick faces? Any comments or references welcome.






RE: Masonry facing
You also need enough vertical masonry above the opening to form a triangular area which peaks below the top of the masonry. We normally use a 1:1 slope on the triangular arch lines.
RE: Masonry facing
http://www.bia.org/html/frmset_thnt.htm
The above is the listing for the Brick Institute of Americas technical listing for note 31B, "Structural Steel Lintels" that shows the loading characteristics that you would consider for any specific configuration, similar to what JAE is refering to. Diagrams are given and you can download their notes for free.