Paralleling 2-cycle and 4-cycle diesel eng gen sets

Paralleling 2-cycle and 4-cycle diesel eng gen sets

Paralleling 2-cycle and 4-cycle diesel eng gen sets

(OP)
"Facts"
Existing facility has three 400 KW 2 cycle diesel engine generator sets and wants to add a fourth 400 KW 4 cycle engine generator.

Pitch of new generator is not same as existing generators, but is "compatible".

Question:
Because 2 cycle engine has a much faster recovery time (from lump loads dropped on paralleled system) than the 4 cycle engine, am I facing circulating current problems?

What problems are likely?

RE: Paralleling 2-cycle and 4-cycle diesel eng gen sets

I do not have much hands-on with generators, but have reviewed some layouts.  With proper monitoring, protection, and syncing before allowing them to close together, as with any multiple source system.  I do not see a problem with engine type.

RE: Paralleling 2-cycle and 4-cycle diesel eng gen sets

The generators probably will not share load transients equally due to the different behaviour. It is not unusualy to operate units of different rating in parallel so I doubt your situation would be a problem. The difference in winding pitch would concern me more. That can lead to circulating harmonic current.

RE: Paralleling 2-cycle and 4-cycle diesel eng gen sets

Suggestion: Contact the Diesel Generator Set manufacturer(s) for tech support.
There are various items that do count during the genset paralleling, e.g.
1. Speed governor control parameters that influence the genset transient and steady state characteristics
2. Automatic Voltage Regulators (AVRs) that influence voltage dips.
3. GenSet Protective relaying schemes
4. Etc.

RE: Paralleling 2-cycle and 4-cycle diesel eng gen sets

I don't see 2-cycle vs. 4-cycle being any kind of problem for normal operation.  As for the winding pitch, if this is a low-voltage solidly-grounded system, you should get assurances from generator supplier as to expected level of third-harmonic currents and any necessary derating of the generators.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources