internal temperature conditions
internal temperature conditions
(OP)
we all know what internal temperature control conditions are, i.e 24degC +-2 etc, but where is it stated that 24 deg.C is the design temperature and that +-2 deg.C is the control range.





RE: internal temperature conditions
TTFN
RE: internal temperature conditions
Eng-Tips.com : Solving your problems before you get them.
RE: internal temperature conditions
RE: internal temperature conditions
TTFN
RE: internal temperature conditions
RE: internal temperature conditions
You still haven't indicated what the exact wording of the specification is.
TTFN
RE: internal temperature conditions
RE: internal temperature conditions
i need to prove to a court that the design of an a/c system is operating incorrectly and to prove what a design condition means, i am looking for a document that can help me prove this from an institution, does anyone know of any?
RE: internal temperature conditions
Even on military systems, we assume that ambient conditions are aggravated by solar load for thermal analysis.
Since the system, in fact, fails to meet its requirements to keep the temperature below 26ºC when the external ambient is below spec value, the question about what is really the design point is essentially irrelevant.
TTFN
RE: internal temperature conditions
Standard thermostat on/off control of unitary AC is +/- 2°F. The AC unit compressor will continue to run till the setpoint temperature is reached. When the space temperature climbs up to 2°F above the setpoint, the compressor runs again till the setpoit is reached. If the space temperature drops 2°F below the setpoint and if the AC is in the heating mode, the heater will run untill the setpoint space temperature is reached. The +/- 2°F is called deadband. The ANSI/ASHRAE/IESNA 90.1-1999 standard now do not dictate indoor. However it tabulates the outdoor design condition (Appendix D-1 to D-3) and calls for +/- 5°F deadband (6.2.3.1.2) except for special occupancy (hospital, retirement home, museaums, process etc) and for thermostats that require manual changeover between heating & cooling mode. Unitary AC with heating or cooling switch fall within this exception. How often & when is the setpoint exceeded?
RE: internal temperature conditions
RE: internal temperature conditions
Are there any ASHRAE, CIBSE guides that reference the above.
RE: internal temperature conditions
Carrier E20 load calculation programme witch uses the ASHRAE method, has an input data setction which asks for design room temperature setpoint and the throttling range. If the room is to be designed at 24+/-2 deg C then the room setpoint is entered as 22deg C and the throttling range is specified as 4 degrees C. I am almost certain that the programme, when sizing the plant allows the room temperature to float to 26Deg C.
If you want more info on that i can email the section in the help menu that explains all that stuff to you.... it is very good and could explain the situation to you better
Regards
Billyq
RE: internal temperature conditions
RE: internal temperature conditions
The 24C +/- 2C belongs in the "desired internal conditions" section, where it should clearly state that this is the desired set point and acceptable limits of control. (+/- 2C is really too much by the way.)
You are not providing much information, which is understandable given the situation. If you are attempting to base your entire case on the +/- thing you seem to be in a pretty weak position.
Have you obtained the contractor's design calculations yet? You lawyer should get these on discovery, but if he hasn't, should subpoena for them. That is where you are most likely to find something to make your case.
Given the apparent lack of consideration of solar gains you might be able to demonstrate that the design calculations did not comply with accepted practice.
RE: internal temperature conditions
the info on the carrier E20 would be very useful, would it be possible for you to send it to me, can you sent it to the below email address.
marktickle@hotmail.com
cheers
RE: internal temperature conditions
If the design documents state that 24*C is design set point then that's what the system should do under all conditions. Set point is always allowed to drift up and down from set pt(deadband/throttleing range)because perfect set point is really impossible to achieve even with DDC Controls. Control point: The actual value of the controlled variable (setpoint plus or minus offset).This from Honeywell
Gray Manual
Roger
RE: internal temperature conditions
Design criteria:
Internal and external are basically the
designer's choice, subject to local code.
Probably (very good idea) chosen from CIBSE /
ASHRAE / other guides.
unless specified in your local code, there is
no black and white requirement. However in some
countries there is a minimum temp. covered my
labour laws.
If I chose a particular internal condition
temp. say 24 deg C, and prep calcs, they are
based on a set of external conditions.
Effectively, I am promising the owner that the
internal temperature, will be *maintained* ONLY
when the external conditions are within my
described conditions.
If unexpected weather conditions drive the
external conditions beyond the design range,
the internal conditions will vary also.
variance, since automatic control systems can't
maintain a single point without excessive
hunting - the designer would specify a
control range say -+/-1 deg C.
A sensible designer would specify, in the
design brief, the "DESIGN conditions" at the
outset.
However, these are NOT 'cast iron' guarantee's
that the internal conditions will be maintained
under every possible circumstance.
If the designer specified 24 +/- 2 deg at the
outset, during specified external conditions,
and there is no other hidden local code
requirement, the designer has achieved the
intent.
One might try to argue, using "best practices",
etc. however legally the designer is probably
safe, depending on documentation :)
my 2 cents
cheers,
RE: internal temperature conditions
the problems associated with the a/c system is that it is not coping with the solar gain, it works fine during overcast days even though the external temp is as high as 40degC, but when the external temp is 32degC and a clear day with direct solar radiation entering the space it is not maintaining the internal design temp.
now the issues i see that i must put forward for my argument is,
a) the design calcs did not take into consideration direct solar radiation, to which i am informed that there are no heat load calculations. (or they don't want to submit them at this stage)
b) the glazing spec was not considered
c) the developer reduced the quality of construction with the view to reduce cost and did not inform the sub contractor,
d) a risk assessment was taken with the cost of installing a lesser system and taking the chance of no tenants taking action
e) the power supply to the building was not sufficient and a probability of consumption taken.
the question i am asking of you is, is there a document that can support my argument that an internal design condition with a tolerance of +/- XdegC means the design calculation is based on X and a tolerance is allowed for the fluctuations in the air system thermostat. i know as well as the rest of you what this means but when i put this forward to a court i must prove my statements which can be done through a document from an institution like cibse or ashrae etc, or through an industry standard calculation methods such as the Carrier method.
i am reviewing the suggestions made from imok2, mintjulip and billyq, hopefully i can put a good case forward.
anymore suggestions are most appreciated, thank you all for your help.
RE: internal temperature conditions
Since the glazing was *known* at the time of
deisgn/installion therefore has no bearing,
unless it was changed?
It is real simple:
The designer (contractor?) failed to provide
adequate cooling to overcome the solar load
at the specified design day, easy enough to
argue using ashrae.
Why bother trying to complicate your case
with tolerance issue? The system tolerance
has no bearing on the real issue, the system
is not failing by 0.25 deg is it?
It will be way to complex, your argue +/-2 deg C,
I would counter with instrument tolerance...too messy.
measured where?
In CIBSE air temperature is not even the criteria
for comfort, which would help you case on a sunny
day.
cheers,
RE: internal temperature conditions
Unless the specification says something to the effect of:
"nominal temperature of 24º with an uncertainty of ±2º"
there is no technical basis for assuming that interpretation. Even as written, it would still be ambiguous whether the tolerance represents the total uncertainty or something like a 1-σ tolerance.
The fact that you've gotten different answers suggests that there is no commonly accepted interpretation for your specification. And, unless there's a statutory or contract requirement, the specification cannot be superceded.
TTFN
RE: internal temperature conditions
I feel if you open that line of enquiry
you would allow the opposition to argue
tolerance mean't floor to ceiling or
day to night, and twenty other excuses.
It would cause confusion, making
your case *appear* weak.
cheers,
RE: internal temperature conditions
The +/- 2 thing is definately too weak to try to base your case on.
It seems clear that the contractor did not calculate the cooling load in accordance with recognized practices. Does the contractor have an PE on staff? You may even have the opportunity to argue that the contractor performed "engineering" without being and engineer.
It also sounds like the spec provided by the consultant is ambiguous.
RE: internal temperature conditions
This is a typical standard practice statement taken from Honeywell Gray Manual
"Properly applied automatic controls ensure that a correctly designed HVAC system will maintain a comfortable environment and perform economically under a wide range of operating conditions. Automatic controls regulate HVAC system output in response to varying indoor and outdoor conditions to maintain general comfort conditions in office areas and provide narrow temperature and humidity limits where required in production areas for product quality".I'm sure you can find much more to bolster your case
Roger
RE: internal temperature conditions
The real question here is what exactly was the contractor's contractual obligation to the client and did he meet those obligations? I am not clear on this based your description so far. What were the conditions of the contract? Was performance criteria assigned? These are the questions that would come up in a court of law.
One last side note, have you run cooling load calculations to identify what the design capacity should have been? Forget any calculations the contractor may or may not have done. This action alone could easily demonstrate quantitatively the deficiency of the cooling system, however, the contractor may not have been under obligation to provide a system to maintain set point if it was not written in the contract documents.
RE: internal temperature conditions
RE: internal temperature conditions
just to let everyone know who commented on this forum that we have won the case, the approach we took was to highlight the fact that the developer did not comply with the specification and therefore not fulfilling their contract. the court agreed with this and now is required to rectify the problem. i'm think this is where the fun starts, tring to get the developer to install something that is correct and fixes the problem should be interesting in itself, but at the end of the day the developer didn't build the building to spec and cut corners to improve profit.
'in your face you penny pinching ba**ards'
thanks again to everyone for thei comments.
cheers
mark.
RE: internal temperature conditions
CIBSE Guides are just that and I would suggest that the ASHRAE guides are the same.
The specification will be the key, although the client will have reasonable expectations that the work will be carried out by a suitably competent person.etc.
I have appeared as an expert witness on design faults and the only winner is the legal team..so its best to resolve the problem amicably.
An expert witness would look at the clients initial brief and the specification.
Also, what temperature has been specified, i.e. is it 'air dry bulb', environmental, 'resultant' etc. There are many thermal indexes to choose from.
Drapes
RE: internal temperature conditions
So, in my view, it is not a matter of what the system was sized for (because the sizing is merely an intermediate step between A (client saying "please design me a system") and B (you delivering a system). Focussing on how it was sized is missing the point.
Also, be VERY careful not to confuse CONTROL range and PERFORMANCE range. If the temperature sensor "kicks in" at say 25, the room will continue to rise in temperature "for a while", in other words there won't be an IMMEDIATE response felt at the point of control.
The room might have some inertia in it so even though the sensor/stat has kicked in at 25, the room inertia might be greater than the "thump" of the cooling system and so the room might get to 26 before it stops heating and starts to cool down.
I'd be asking - how is it performing? If it performs such that the room oscillates between 26 and some temperature below 26, then I'd say you've met the hardest part of the 24 +- 2 degC. The system should be capable of getting the room to 24 for "most of the time", (and so I would size the system based on 24 deg C internal absolute, then ADD soem % or whatever to account for inertia).
Any help ??
Paul K
PS - Jeez Billy Q, with an intellect like yours, maybe you should come work for me ..... (private joke, apologies to others, I'll post my CONSIDERED response later).
PS Billy, please send cheque in the amount of $895 + GST for Civic dampers ordered H x W instead of W x H .....