PVC in High Rise Buildings

PVC in High Rise Buildings

PVC in High Rise Buildings

(OP)
A 40 story building has 30 office floors and 10 parking floors. Offices are Light hazard and parkings are Ordinary hazard 1.  A listed plastic pipe can be used in office floors?.

RE: PVC in High Rise Buildings

Correct, you can use plastic pipe on the office floors.  However, plastic pipe becomes a nightmare when you have to do tenant remodel as tenants come an go.  If any way possible, I would recommend steel.  It will make it much easier for the build outs later on.  Also, with a building that high, you will have significant pressures at the lower levels.  Be sure to avoid a series of 1" grid branch line piping on the lower floors.  You can't use a mechanical tee to supply heads for the build outs down the road.

RE: PVC in High Rise Buildings

PVC Pipe for electrical work or mechanical work?

RE: PVC in High Rise Buildings

(OP)
Can I use SCH 10 pipe in each floor and SCH 40 in riser? The static head in some floors is almost 250 psig.

RE: PVC in High Rise Buildings

Yes...there is no reason that you couldn't use Sch 10 on the floors and Sch 40 in the riser...however, why?  ..with the steel shortages (if you are in the US), Sch 40 is getting very tough to come by.  Sch 30, 10 and 7 are rated for 300 PSI.  I would say Sch 10 or 7 for the grooved piping and Sch 30 (one brand name DynaThread)for the threaded line piping.  Use pressure reducing control valves at each floor where the pressure is in excess of 175 psi.

RE: PVC in High Rise Buildings

(OP)
I will use ECOH sprinklers heads (K=11.2)in parkings floors. I need help in sizing the pipe.

RE: PVC in High Rise Buildings

It requires you to perform hydraulic calculations to size the piping.  You will want a software program to do that.

RE: PVC in High Rise Buildings

Be careful about using PVC piping in the plenum of the spaces, as it usually doesn't meet fire codes if the plenum is used for the return air.  

RE: PVC in High Rise Buildings

Per the Blazemaster listing, PVC can be used in plenums as noted:
"Return air plenums with no set-back at ceiling openings per NFPA 90A "

RE: PVC in High Rise Buildings

Another consideration regarding PVC piping on the upper floors is that the pipe itself requires much more hanger support.  Sometimes the spacing of the steel is such that it becomes larbor intensive.  You can use drop in anchors (if the spec allows it)but still there will be many of them.

RE: PVC in High Rise Buildings

correct...the hangers are an issue.  With the advent of the Sammy Xpress hanger, it is becoming less of a problem on upper floors.  Also, with the volatility and availability issues of steel piping, I think we may be seeing more plastic jobs being installed.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources