Maximum No. Of Systems from Ring Main Spur

Maximum No. Of Systems from Ring Main Spur

Maximum No. Of Systems from Ring Main Spur

(OP)
Can anyone please advise me if there is a restriction on the number of Fixed Fire Protection Systems (Deluge Waterspray)that can be supplied from a spur off a Yard Ring Main.

I thought there was something in NFPA 850 but I can't find it, my concern is the number of systems that may be isolated simultaneously.

RE: Maximum No. Of Systems from Ring Main Spur

There is nothing that I am aware of that limits the number of systems being supplied by a single lead in.  If I recall correctly, I believe that Factory Mutual recommends no more than 4 risers...but that could be old information.

We typically try to limit to 4 or 6 risers.  Simply because the cost to run overhead bulk piping for any more systems will exceed the cost for an additional lead-in to the building from the underground loop.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources