Grounding on Ships

Grounding on Ships

Grounding on Ships

(OP)
I have a project to build a control panel for a ship. The incoming supply is 440 V: 3 phase: 3 wire: 60Hz. I need a 220 volt supply for the control circuit and some little single phase motors and other small single phase loads. I shall fit a double wound transformer to obtain the 220 volt supply. Do I ground one leg of the secondary winding of the transformer to the metal work of the control panel enclosure, and hence the hull of the ship, or leave it floating? In other words, is the sea a good enough ground? If the secondary leg is left floating, it will have to be protected with a fuse or MCB presumably?

RE: Grounding on Ships

I assume that the secod side of the Tx is star connected with a neutral which should be connected (earthed) to the ships hull.

Then you will have 220V ( 1 ph supply) between L-N for your small power distribution.
You must also ensure that all single phase  supplies feeders have 2 core cable connection ie L-N.
You must not use the ships hull as the N return path.
loads such as motors/control panels may be earthed (bonded) locally to ships hull.

RE: Grounding on Ships

Suggestion: Follow the project specifications and/or industry standards, e.g.
IEEE Std 45
Military Standards and Specifications
etc.

RE: Grounding on Ships

(OP)
The incoming supply is 440V 3 phase 3 wire with no neutral. But we need a single phase supply for small loads. This supply we must provide from the control panel using a transformer. Do we ground one leg of the secondary winding?

jbartos thanks for tip on IEE STD45.

RE: Grounding on Ships

Kevd seems to be pretty informative on this subject...

See Earthing in Ships - Thread238-51057...


RE: Grounding on Ships

(OP)
Thank you all, I believe that between you,you have solved my query. I did search for previous threads but couldn’t find any. However, "tulum" pointed me in the right direction thanks!

“There’s none so blind as those who will not look!”

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources