Help required regarding info on EN60204 14.2 Cable colour codings (UK)
HI.  Can anybody help regarding info on cable colour codings in accordance to EN 60204 14.2 standard. In particular relating to 415V 3PH electrical control panel wiring, 24V AC and DC control circuits, and for systems destined for the UK.
Any help on this would be most appreciated.
Cheers. John.
RE: Help required regarding info on EN60204 14.2 Cable colour codings (UK)
BS7671 2001 "Requirements for Electrical Installations" IEE Wiring Regulation Sixteenth Edition
TABLE 51A - Colour identification of cores of non-flexible cables and bare conductors for fixed wiring
Function
protective conductors                      Green-and-yellow
Phase of a.c. Single-phase cir.                  RED
Neutral of ac 1ph & 3 PH                        BLACK
Phase R of 3 PH                                  RED
Phase Y of 3 PH                                  YELLOW
Phase B of 3 PH                                  BLUE
Two-wire unearthed d.c.
Positive                                          RED
Negative                                          BLACK
Three-wire d.c.
Outer(positive or negative) of d.c.
two-wire circuit derived from 3-wire              RED
Positive of 3-wire d.c.                           RED
Middle wire of 3-wire d.c.                        BLACK
Negative of 3-wire d.c.                           BLUE
2-wire earthed d.c.
Positive(of negative earthed)                     RED
Negative(of negative earthed)                     BLACK
Positive(of positive earthed)                     BLACK
Positive(of positive earthed)                     BLUE
Functional Earth                                  Cream
If you are wiring to EN 60204-1, then in my opinion the colours stated above do not apply.  I agree they are used regularely in field wiring and installations etc, but for control panel wiring EN60204-1 states:
"It is recommended that insulated conductors be colour-coded as follows:"
 - BLACK:    a.c. and d.c. power ccts;
 - RED:      a.c. control ccts;
 - BLUE:     d.c. control ccts;
 - ORANGE:   interlock control ccts supplied externally.
A lot of authorities have there own standards to wire to (ie Water, Petro-chem etc), that will deviate from EN60204-1.
Post your email, and i can send you the page from EN60204-1 relating to these colours (there are notes relating to the Neutral etc).