Safety Relief valve sizing

Safety Relief valve sizing

Safety Relief valve sizing

(OP)

When sizing a Thermal relief valve to API 520 & 521 (Fire case), what is the value for the 'F' factor, when an insulation material is not classed as having passive fire protection. The vessel is insulated and rated up to 120 Deg C.

Should the factor be 1 for a non insulated vessel or 0.3 based on an insulated vessel.

Thanks
KAL

RE: Safety Relief valve sizing

NFPA 59 section 7 will provide additional guidance on environmental factors. I'm going from memory here, but I'm almost certain that you will need to use 1.0 because in order to use a factor less than 1.0, the insulation must be able to maintain integrity during a fire condition.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources