Pressure Test of motor water-to-air coolers (heat exchangers)
Pressure Test of motor water-to-air coolers (heat exchangers)
(OP)
Could anyone point out to websites that give the detailed procedure for hydraulic pressure test of water-to-air coolers (heat exchangers) ? Thx in advance





RE: Pressure Test of motor water-to-air coolers (heat exchangers)
Visit
http://www.1stindustrialdirectory.com/Heat_Exchangers/Heat_Exchangers_25.html
etc. for more info
RE: Pressure Test of motor water-to-air coolers (heat exchangers)
Sorry I do not have any standard. We test the water circuit applying water at 6.2 to 6.9 Bars (90 to 100 psi) for one minute.