Horizontal reinforcing in concrete block wall
It seems popular to use vertical reinfocement in conc block masonry walls. Horizontal reinforcement is used, as far as I know, for lintels and for joint reinforcement as well.
I have a situation that a non-loadbearing exterior wall needs reinforcing against wind load. Apparently using horizontal rebars is more effective since the wall has steel columns backing-up. Can anyone advise whether standard reinforcement bars are used horizontally? Is it as effective as the vertical ones?
Thanks in advance.
p.s. if it's okay, should the rebars be in pair to be placed under the face shells?
Thanks in advance.
RE: Horizontal reinforcing in concrete block wall
The spacing of these bond beams is up to you, it just adds to the flex in the bond beam. Between bond beams we assume that the wall spans vertically and reinforce vertically as well. Sort of a two-way action wall.
DaveAtkins
This has a longitudinal bar to each face of the masonry unit, so each layer of reinforcement acts to deal with wind pressure or suction.
It is available in galv. or stainless steel, and is laid every course or every other course, depending on your applied wind loads.
It is also used to increase the length required between expansion joints, as the reinforcement helps to deal with expansion and contraction forces.
Hope this helps!
Since the steel beams/struts are also behind the wall(not touch because the columns are pretty thick), I'll utilize them, with anchors along the beams to CMU, to provide lateral support. The two-way action is formed as well. By this approach, I don't need concern the control joints.
If I read your post correctly we call it dura-wall.
DDS1