SEPARATION OF DIFFERENT CABLES

SEPARATION OF DIFFERENT CABLES

SEPARATION OF DIFFERENT CABLES

(OP)
The Owner is not ready to invest for new Cable Tray.The new 5 kV cable is provided to be installed ( small section only)together with -
 600 V existing power cables
 24 V DC existing signalisation cables
The Engineer working for Owner says that is acceptable. But that is not ... acceptable.

RE: SEPARATION OF DIFFERENT CABLES

Don't all the cables in a cable tray have to be rated for the voltage rating of the highest cable?...



RE: SEPARATION OF DIFFERENT CABLES

Usually power cables (5kv (and up)) are kept in trays by themselves.
600vac, 250vdc, 240vac, 125vdc, 120vac are usually grouped together ac a voltage group.
Instrumentation go in separate trays.

RE: SEPARATION OF DIFFERENT CABLES


For ANSI regions, review 2002 NEC Article 392 as a minimum standard.  IEEE Std 141 {red book} §12 is another reference.
  

RE: SEPARATION OF DIFFERENT CABLES

Medium Voltage (MV) cables may be installed in the same tray as 600V or less cables per NEC 2002 392.6 (F).

However, I would not mix MV and Controls in the same tray unless spacing and shielding were looked at VERY closely.

RE: SEPARATION OF DIFFERENT CABLES

It is better of course if there is a separation between the dc cable and the 5kV cable of say 300mm.
If the eng is adamant that it would be ok to run them in the same tray then one can argue that there may not be any problems with the inteference induced in the dc cable and that all will be well.
If you have to abide by his ruling then  you should  ensure that the 5kV cable is furthest away from the dc cable and hope for the best on that basis that should you experience problems in the future then you can alays rerun the 5kv cable in a new adjacent tray. To allow for this you should allow for the 5kV cable with some slack to ensure that it can be re run to suit.
On the assumption that all cables are armourd or screened, you might just get awa with it.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources