XLPE Cable Ampacity

XLPE Cable Ampacity

XLPE Cable Ampacity

(OP)
1) I just want to know if an XLPE cable on a ladder type cable tray inside a plant can be considered installed in "free air"?  2) Is there any difference in ampacity of a 250 mm sq XLPE Cable rated at 15kV when installed in 4160V system (consider indoor application)?
Thank you guys in advance.

RE: XLPE Cable Ampacity

The cable gets the free air rating as long as the spacing is 1 cable diameter or more.

You should use the 15KV ampacity rating because the insulation provides thermal insulation to the copper whether it is electrically required or not.

As an aside, you have to watch yourself with XLPE in tray because it usually doesn't have sufficient fire rating without armour at 15KV.  To get an unarmoured cable with suffcient fire rating for indoor tray, EPR is often required.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources