How to calculate transformer heat loss

How to calculate transformer heat loss

How to calculate transformer heat loss

(OP)
I am trying to figure out what the heat gain would be for a 250kVA transformer.
I have done several searches here and thru google and have not found corroborating info on the calculation.
One site calculates the heat gain as:

Heq = PeqK1K2    (W)
where
Heq = heat transferred from electrical equipment   (W)
Peq = electrical power consumption (W)
K1 = load coefficient
K2 =  running time coefficient

and others use a rule of thumb between 1% and 5% of rated load.

Can anyone point me to a calculation that I could reference? I have searched thru my ASHRAE handbooks but have not been able to find anything.

RE: How to calculate transformer heat loss

What you need to find out is the efficiency of the transformer and how heavily loaded it is. Then consider the transfrmer like a motor in the space but the driven equipment as being out of the space. The heat gain to the space therefore is:

watts heat gain = ((1/eff)-1)x(Kw input) x 1000

Efficiency ranges from 90% for small transformers to 98% for large transformers. You have to get manufacturer's data. Efficiency may vary w/ % loading.

Transformers typically can tolerate a maximum of 104°F but check with manufacturer. If you exhaust high over the equipment & supply air low, by stratification you may be able to reduce air supply required. But it is better to be safe than designing it too close.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources