Expansion joint in 2'-8" foundation slab?

Expansion joint in 2'-8" foundation slab?

Expansion joint in 2'-8" foundation slab?

(OP)
I am working on a project with a pump station and water tanks sitting below grade. Due to buoyancy, I need 2'-8" thick base slab. Due to length of structures, I need 1 inch expansion joint in this slab. I will use PVC waterstop.

I just can not find any ideas or info on how to leave this 1 inch open under the waterstop. If I use any filler, it will be smashed by the concrete during pour.

Any ideas?

RE: Expansion joint in 2'-8" foundation slab?

I'm curious why you need a 1" expansion joint if this is below grade?

RE: Expansion joint in 2'-8" foundation slab?

(OP)
Top of tanks and pump station is above grade and with winter-summer temperature changes it will move or brake.

RE: Expansion joint in 2'-8" foundation slab?

Where is your site?



Please see FAQ731-376 for great suggestions on how to make the best use of Eng-Tips Fora.

RE: Expansion joint in 2'-8" foundation slab?

(OP)
OK, I talked to void forms people and they said that they may provide 1 1/2 inch void form. So I will use 1 1/2 inch joint.

Thanks.

RE: Expansion joint in 2'-8" foundation slab?

We use a sponge rubber or asphaltic filler, a round backer rod at the top of the joint, a bond breaker and caulk the joint with a two-part polyurethane sealer.  The concrete will not crush the filler.  Don't forget, you're only talking about 32 inches of liquid concrete "head" and these filler are pretty stiff.
You want to make sure that stuff doesn't get in the joint and restrict the movement.  Hence the backer rod and caulk.  If the void forms you're talking about are the same I'm familiar with, they'll deteriorate and you'll be left with an open gap.  This will quickly foul with grit and dirt and stop the joint from closing.
See ACI 224.3R Chapter 9 for some examples.

RE: Expansion joint in 2'-8" foundation slab?

We have made foundation (cellar) mats for buildings over 1 m thick and 120 m long (also of lesser thickness and horizontal dimension) without any special provision for joints in the mat and has not caused any problem. Underground vases may or may not require the joints. Walls use to be far more critical than the mats. In any case, engineered joints shouldn't cause any problem either and with proper consideration of what ongoing may be from required to simply part of a better designed structure.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources