Embedment of Railing's PostS in Concrete Slab
I am looking for a good reference or a tip to design the embedment of aluminum or steel guardrail's posts in concrete slab. The post as per local codes is subject to a lateral load of 200lb or it could be much higher if the post is a member of an exterior glaized railing where the system is subject to wind loads. I have seen other engineers using formulas that I am not familiar with and I could not locate any reference material on these formula.
a= 2 M^2 + 3L.M /3M + 6L
P2= a^2 x P / [M(2a-M)]
M is the embedment length of the post in the concrete slab
L is the height of the guardrail post
P is the lateral load applied on the top of the post described abve
P2 is the resisting force to P below concrete slab
RE: Embedment of Railing's PostS in Concrete Slab
Can you briefly explain this section. I do not have this code but I am willing to purchace if this section is related to my question.
Andy Machon
You had already mentioned this manual. I sill cannot find it. What do you mean by the Steel Construction Institute? I couldn't find this assiciation. Do you meaan AISC? Can you give me contact information.
Thanks.
ubc '97 states:
The following two formulae may be used to determine depth of ebbedment.....
d=A/2(1+(1+4.36h/A)**1/2)
d*2=4.25Ph/$b
where: A=2.34P/^b
b=diameter or diagonal of post in feet (m)
d=depth of embedment
h=height of load
P=applied load
^=allowable lateral soil-bearing pressure as
set forth in table 18-I-A based on a depth of
1/3 the depth of embedment
$=allowable lateral soil-bearing pressure as
equal to the depth of embedment
The first formula is for the non-constrained condition
(post in unpaved soil)
and second formula is, I believe, your case....where the surface is paved.
In the first formula you have to play around with "d" and "A" until you get a "d" (or an "A" but in most cases it will be "d") that you can live with.
Steel Construction Institute is a British organisation.
See http://www.steel-sci.org
and follow the links Courses & Publications...Publications...Index by Subject Category...General Publications on Structural Steelwork
Other UK/European steelwork stuff is in the Corus website
http://www.corusconstruction.co.uk
Corus Group plc was formed in October 1999 by the merger of British Steel and Koninklijke Hoogovens of the Netherlands. The Corus site has various on-line design resources and provides links through their 'Organisations' page to SCI (Steel Construction Institute) and BCSA (British Constructional Steelwork Association), so tag this site if you want to keep a bookmark to UK steel practice.
regards Tom