Environment Control for Small Spaces
Do you guys have any suggestions for what type of equipment would be able to accurantely maintain the temperature and humidity in a small display cabinet.  The cabinet will be approximately 4 ft. x 4 ft. x 8 ft.  It will not have any solar gains.  It will have a historically significant plaster statue (person sized) inside.
RE: Environment Control for Small Spaces
Grizzly68 I suggest you ck with the local morgue!
Grizzly, Liebert probably has something. Can you maintain the needed conditions in the space that houses the chamber, or is it in a huge hall?  Regards, CB
CB,
No, i can't condition the existing space.  That would require renovation of the HVAC system for the building.  I've checked with Liebert and they don't have anything small enough.  The only thing I can think of is something that might be used by museums.
I wonder if I would even need to humidify.  If the artifact will be sealed up, with the only porous surface being the wood base then humidification/dehumidification might not be a concern.
Grizzly
Griz,
Try Ice Qube.  They make some pretty small and neat-looking control cabinet coolers.  If you need to humidify, look for Dri-Steem.   If dehumidification is needed, you might need to oversize your cooler a bit and add reheat.  Hoffmann has nice, small cabinet heaters.
Here are web sites:
www.iceqube.com
www.dristeem.com
www.hoffmanonline.com
Best of luck!
DRWeig
Grizzly68
You do not state the conditions that are required. If you can tolerate 10 to15 degrees below your ambient (within limits) you might consider thermoelectric refrigeration.
That is solid state cooling (Peltier Effect).  Very small refrigerators are on the market today using this technology. You might do the same using multiples.
Keeping the container sealed and back filled with nitrogen gas would reduce the moisture and refrigeration load. I am sure you do not want condensation forming on the inside or the outside of the container. Thermoelectric’s reduce the impact to your installation because you only need an electrical source. No piping, no condenser airflows, no chilled water to leak…
A google search Thermoelectric Refrigeration rendered over 6000 hits and a search; Peltier Effect came up with over 38,000.
More information would help us all to understand your needs
Good Luck
pennpoint
One shot and two birds, check with www.drykor.com. This is basically a dehumidifier which uses heat rejected by the refrigerating cycle to reactivate desiccant and air is cooled in the evaporator section.
Eng-Tips.com : Solving your problems before you get them.
Thanks for your feedback guys.
Chris