Water quality of bolier

Water quality of bolier

Water quality of bolier

(OP)
Dear all,

Can anyone provide some information about the water quality inside a boiler of a CCGT facility. Any good books and standards (British standard, German Standard....) refer to this area.

What are the general parameters which defined the water quality? e.g. Oxygen content, pH, Silica, Fe..........

And also what is the difference between Conductivity and Cation Conductivity?

Thanks

Frederick Chan


RE: Water quality of bolier

Fred,

An organization called the ABMA ( American Boiler mf'rs Association) publishes a standard detailing boiler water and steam quality.

see page 4 of this .pdf:

www.esitenn.com/news/newsletter/issue18.pdf

Also see:

www.cip.ukcentre.com/steam.htm

Additionally, your CC steam turbine mf'r may have standards that are different or more restrictive.

MJC

  

RE: Water quality of bolier

a) You can consult the standard VGB R 450 L (German, www.vgb.org ) for information on Boiler feed water, Boiler water and steam characteristics.

b) ASME has information (http://members.asme.org/catalog/ItemView.cfm?ItemNumber...) which perhaps is interesting for you.

Please be aware that the German recommendations (higher requirements) are different than the ASME recomendations.

When you measure specific conductivity you will measure all ions contained in the water.   Cation conductivity is measured after a cation ion exchanger

RGS

RE: Water quality of bolier

Hello,
There is a reference for us which has to be amended according to your plant conditions and the discussions you should have with your boiler and turbine manufacturers. It comes from EPRI and is the counterpart of CS 4629 which is talking about fossil fired plants.

Interim Cycle Chemistry Guidelines for Combined Cycle Heat Recovery Steam Generators (HRSGs)
TR-110051 - 01/28/1998 - 04T079.0.

This is "giving" to you recommendations for water and steam quality in the different nodes, as well as rationales for this, for a CCGT. The only problem is that they are pricing that 12000 USD. Otherwise, you should just follow GE recommandations, they are just following that standard. (you should also have a look on "Steam" from B&W).

RE: Water quality of bolier

Hi,
I hope this will help you

TO ASSURE GOOD QUALITY OF STEAM. S. NO    BOILER PRESSURE(PSIG)    TOTAL DISSOLVED(TDS)    ALKALINITY(PPM)    SILICA(PPM)
01    0-300    3500    700    125
02    301-450    3000    600    90
03    451-600    2500    500    50
04    601-750    2000    400    35
05    751-900    1500    300    20
06    901-100    1250    250    8
07    1001-1500    1000    200    2.5
08    1501-2000    750    150    1.0
09    ABOVE 2000    500    100    0.5
ALWAYS KEEP WATER PARAMETERS UNDER LIMITSGET MAXIMUM EFFICIENCY INCREASE YOUR PROFITS
TO ASSURE GOOD QUALITY OF STEAM. S. NO    BOILER PRESSURE(PSIG)    TOTAL DISSOLVED(TDS)    ALKALINITY(PPM)    SILICA(PPM)
01    0-300    3500    700    125
02    301-450    3000    600    90
03    451-600    2500    500    50
04    601-750    2000    400    35
05    751-900    1500    300    20
06    901-100    1250    250    8
07    1001-1500    1000    200    2.5
08    1501-2000    750    150    1.0
09    ABOVE 2000    500    100    0.5
ALWAYS KEEP WATER PARAMETERS UNDER LIMITSGET MAXIMUM EFFICIENCY INCREASE YOUR PROFITS



RECOMMENDED ABMA & ASME BOILER WATER LIMITS                                        DRUM OPERATING PRESSURE (psig)
      0-300     301-450     451-600     601-750     751-900     901-1000     1001-1500     1501-2000     OTSG
STEAM                                                       
TDS max (ppm)     0.2-1.0     0.2-1.0     0.2-1.0     0.1-0.5     0.1-0.5     0.1-0.5     0.1     0.1     0.05
BOILER WATER
TDS max (ppm)     700-3500     600-3000     500-2500     200-1000     150-750     125-625     100     50     0.05
ALK. max (ppm)     350     300     250     200     150     100     Not specified     Not specified     n/a
TSS Max (ppm)     15     10     8     3     2     1     1     n/a     n/a
Conductivity max (µmho/cm)     1100-5400     900-4600     800-3800     300-1500     200-1200     200-1000     150     80     0.15-.25
Silica max (ppm SiO2)     150     90     40     30     20     8     2     1     0.02
FEED-WATER (CONDENSATE & MAKEUP, AFTER DEAERATOR)
Dissolved Oxygen (ppm O2)     0.007     0.007     0.007     0.007     0.007     0.007     0.007     0.007     Not sensitive
Total Iron (ppm Fe)     0.1     0.05     0.03     0.025     0.02     0.02     0.01     0.01     0.01
Total Copper (ppm Cu)     0.05     0.025     0.02     0.02     0.015     0.01     0.01     0.01     0.002
Total Hardness (ppm CaCO3)     0.3     0.3     0.2     0.2     0.1     0.05     None detected     None detected     None detected
pH @ 25º C     8.3-10.0     8.3-10.0     8.3-10.0     8.3-10.0     8.3-10.0     8.8-9.6     8.8-9.6     8.8-9.6       
Nonvolatile TOC (ppm C)     1     1     0.5     0.5     0.5     0.2     0.2     0.2     None detected
Oily Matter (ppm)     1     1     0.5     0.5     0.5     0.2     0.2     0.2       
MAKE-UP AT 0.5% BLOWDOWN
TDS     11.4     9.8     8.1     6.5     4.9     3.3     0.5     0.3       
Silica (ppm SiO2)     0.75     0.45     0.2     0.15     0.1     0.04     0.01     0.005       
MAKE-UP AT 1% BLOWDOWN
TDS     22.8     19.5     16.3     13     9.8     6.5     1     0.7       
Silica (ppm SiO2)     1.5     0.9     0.4     0.3     0.2     0.08     0.02     0.01       
MAKE-UP AT 2% BLOWDOWN
TDS     45.5     39     32.5     26     19.5     13     2     1.3       
Silica (ppm SiO2)     3     1.8     0.8     0.6     0.4     0.16     0.04     0.02       
MAKE-UP AT 3% BLOWDOWN
TDS     68.3     58.5     48.8     39     29.3     19.5     3     2       
Silica (ppm SiO2)     4.5     2.7     1.2     0.9     0.6     0.24     0.06     0.03       


RE: Water quality of bolier

Fred,

to get a proper idea about the conditioning regime, you first have to tell more about the type of boiler (pressure, temperature, what materials is the boiler including the condensor made of etc.). Then of course there is the question which quality of water you produce in your demin plant (take care of silicate, chloride, TOC etc).
There are several regimes available to choose from. You can use simply ammonium as conditioning agent (all volatile treatment), or if you have an extremely good quality water you can use combined treatment (oxygen and ammonium) or even oxygen treatment.

Take one advise from me, avoid organic amines. These will decompose in organic acids which will return in the first condensate on your turbine blades.

My company (KEMA) has issued its own guidelines for water/steam conditioning. The requirements are even higher than the German (VGB) ones but they have resulted in an extremely low number of problems in the Dutch power plants.

If you want more information, just ask.

Best regards,

Edwin

Edwin Muller
KEMA Power Generation & Sustainables
Arnhem, The Netherlands
E-mail      e.f.muller@kema.nl
Internet: http://www.kema-water.nl
http://www.kema.com

RE: Water quality of bolier

Fred,
forgot part of your question. Cation conductivity is the conductivity after passing a cationic ion exchanger. It is a more sensitive reading than conductivity (a hydronium ion has a larger specific conductivity than the other ions.
If you like advise on treatment of your boiler feed water, offer more details. Since it strongly depends on the boiler design, I cannot give you general advise.

Best regards,
Edwin

Edwin Muller
KEMA Power Generation & Sustainables
Arnhem, The Netherlands

RE: Water quality of bolier

It is very important that you verify your ST requirements. Most of the time you have more restrictios with steam quality in the ST that in the HRSG or in the Boiler. The Siemens-Westinghouse clas G (gas turbines) also will require an exceptional steam quality for cooling in the TP and Total Volatil treatment (No Phosphate)
SiO2< 5PPB;
 Cation Cond < 0.2umhos
 Sodium <5 PPB and very low levels of Iron.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources