Is there any value in doing a 5000 volt PI test on a 13.8 kv motor. Even if the readings are trended?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
PI testing on 13.8 kv motors
|
RE: PI testing on 13.8 kv motors
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
RE: PI testing on 13.8 kv motors
RE: PI testing on 13.8 kv motors
VLL(vac) Test Voltage (vdc)
==== =========
<1000 500
1000-2500 500-1000
2501-5000 1000-2500
5001-12000 2500-5000
>12000 5000-10000
5kvdc test of 13.2kv machine is consistent with these guidelines. We use 10kv test at our plant. I don't think using 5kv would be a big problem (there may be slight tip-up if contamination is present). Most important thing for trending is to use the same voltage each time.
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
RE: PI testing on 13.8 kv motors
See Thread " Generator PI Value Problem" 01/10/04 by edison123.
RE: PI testing on 13.8 kv motors