Common Usage of LFMC, LFNC

Common Usage of LFMC, LFNC

Common Usage of LFMC, LFNC

(OP)
NEC Articles 350.10 and 356.10 both use the language "Where conditions...require flexibility or protection of liquids..."

In common practice, is this interpreted as only device which need to move or vibrate are allowed to be connected with flexible conduit, instead of rigid or thin-walled conduit?

Or is it allowed more liberally, that saving labor and difficulty is a good enough justification to use flexible conduit to connect devices?

Thanks for any insight,

Evan

RE: Common Usage of LFMC, LFNC

NEC Articles 350.10 and 356.10 both use the language "Where conditions...require flexibility or protection of liquids..."

In common practice, is this interpreted as only device which need to move or vibrate are allowed to be connected with flexible conduit, instead of rigid or thin-walled conduit? Yes

Or is it allowed more liberally, that saving labor and difficulty is a good enough justification to use flexible conduit to connect devices? No!

See Article 90 .1,.5,.6, Article 110  .1,.2,.3,.8,.11,.12

RE: Common Usage of LFMC, LFNC

(OP)
Is there any difference in this answer for industrial machinery applications, as opposed to facility wiring, does anyone know? I've seen lots of devices connected with sealtite, like switches, solenoid valves, etc. that don't physically move, so I'm just wondering what the typical justification is.

Thanks again,
-Evan

RE: Common Usage of LFMC, LFNC

Is there any difference in this answer for industrial machinery applications, as opposed to facility wiring, does anyone know? No
The problem is if the local AHJ inspection at installation
that wiring method may not be in compliance with the code.
The AHJ my give you some relief if the wiring method is not a flagrant  violation. By this I mean if rigid raceway could not have be used is place of this non approved method.
I've seen lots of devices connected with sealtite, like switches, solenoid valves, etc. that don't physically move, so I'm just wondering what the typical justification is.

These items can be adjusted such limit switches, valve coils
can be removed from their base for service.




RE: Common Usage of LFMC, LFNC

NFPA 79 is used for Industrial Machinery and it permits the use of liquidtight flexible conduit and/or multiconductor cable (see section 16.3 Machine wiring).


David Baird
mrbaird@hotmail.com
 
Sr Controls Engineer

EET degree.

Journeyman Electrician.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources