MCCB single pole ratings

MCCB single pole ratings

MCCB single pole ratings

(OP)
UL 489 and IEC (I think) specify single-pole full voltage short circuit test current for three pole molded case circuit breakers which are much lower than the 3-phase interrupting rating. For example, 1200A frame 3-pole breakers are tested at 12.1kA for full voltage across one pole per UL, regardless of the marked AIC rating.

Corner-grounded systems require the ability for any one pole of a 3-pole breaker to interrupt faults at line-to-line voltage and 87% of rated interrupting current. Does anyone know of a manufacturer of MCCBs tested or rated for line-to-line voltage across a single pole?

RE: MCCB single pole ratings

You might want to check with Square D.  I seem to recall that their breakers are tested for this.  

RE: MCCB single pole ratings


It may be worth mentioning that, besides corner-grounded systems, midtap-grounded 480?/240-volt and 480-volt high-resistance-grounded systems also need the single-pole overcurrent withstand ratings applied.

Another related caveat is that 300-volt fuses applied to a corner-, midtap- or resistance-grounded 480-volt system is also a serious misapplication.
  

RE: MCCB single pole ratings

(OP)
Thanks. I'll give SqD a call. This is an installation that one of my clients just finished. The breakers are GE type SKLB.

I think in the case of resistance-grounded or ungrounded systems, the situation can only occur if there are two L-G faults with one upstream and one downstream of the breaker.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources