Primary Distribution Voltages in California
5

Primary Distribution Voltages in California

Primary Distribution Voltages in California

(OP)
Our company is evaluating the feasibility of supplying some temporary equipment into the California area around Fresno that will reqire a source of electricity at primary (above 750 volt) levels. Can anyone tell me what the predominant primary distribution voltages are in California? For example, 12.5 kV, 13.8 kV, 25 kV, etc. Who would we contact to source the power and provide transformation to the voltage levels we require and at the kVA levels we require?

Thank you, Doug from Canada

RE: Primary Distribution Voltages in California

2

The area is likely served by Pacific Gas and Electric—probably 12000Y/6930 or 20780Y/12000.

Their boilerplate is §B in www.pge.com/tariffs/pdf/ER2.pdf
  

RE: Primary Distribution Voltages in California

34.5kV is common in the Los Angeles area.

RE: Primary Distribution Voltages in California

Having once worked in Fresno, busbar is very close.  The two likely voltages are 12000V delta and 20780Y/12000V, with the remaining 12000V slowly being converted to 20780Y/12000V.  As temporary installations, you are likely to get one or the other and not have to worry too much about it changing.  Any permanent installation in 12000V territory should be designed with the capability (dual primary rated transformers) for conversion to 20780V.

RE: Primary Distribution Voltages in California

A recent project I worked on in Santa Clara was also 12.0kV.

RE: Primary Distribution Voltages in California


Aside — In NorCal a rule of thumb for larger data centers is 600 amperes for feeders, as a load limit for 12 or 21kV distribution circuits.  For larger loads, subtransmission or transmission  voltage is needed.
  

RE: Primary Distribution Voltages in California

(OP)
Thanks again, everyone! It seems like 12/21 kV is the most likely. We are trying to make contact with the utility in Fresno at the moment. In our area here in Canada we have a combination of old 12.5Y/7.2 kV and new 25Y/14.4 kV systems. BC Hydro is upgrading to the higher voltage system, but you'll note that the new system is a 2 times multiple of the old. Thus, most of our existing equipment will not tap down far enough to reach the new 21 kV system being installed in Fresno. However, if it turns out that we are located on an older feeder at 12 kV, we can tap down from our 12.5 kV voltages to reach 12 kV comfortably. We'll keep our fingers crossed. Thanks again to everyone who responded.

RE: Primary Distribution Voltages in California

Suggestion: Considering the temporary power for the temporary equipment, it may be a good idea to check with the Fresno Utility, whether or not the more standard voltages elsewhere, e.g. 13.8kV, are available and can be provided.

RE: Primary Distribution Voltages in California

Standard voltage somewhere is what the utility provides at that location.  In Fresno the standard voltages are 12kV and 20.78kV (referred to locally as 21kV).  13.8kV is not a standard and would not be available, why would the utility build a special substation just to serve a temporary load?  It's just not going to happen.  In fact, as a temporary load, you will pay all utility costs, there will be no line extension allowances or credits as the loads won't be there long enough for the utility to recover their costs.

RE: Primary Distribution Voltages in California

Comment: The Utility can provide non-standard voltages if applied for and paid for.
http://www.rp-l.com/commercialrates.htm
for:
Should the Customer require a non-standard voltage, Customer shall, at his own expense, furnish and maintain all transformers and protective equipment therefore necessary in order to obtain such nonstandard voltage.

RE: Primary Distribution Voltages in California

jbartos, what relevance does a Richmond Indiana utility have to a question about utility practices in Fresno Ca?  Sure, if you want to define it broadly enough, the utility will provide 13.8kV if you are willing to pay for a 12kV (or 21kV) to 13.8kV transformer.  But what's the point if the 13.8kV is then just going to be transformed down to another utilization voltage?  What is gained by the second level of transformation?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources