ControlLogix Tag names & wire#'s

ControlLogix Tag names & wire#'s

(OP)
Need to know how others are coming up with their I/O wire#'s when using Rockwell ControlLogix PLC's.  We're starting to do more of these systems and need a wire # that is easily searchable in the program and also works for as a wire label (it's hard to print more than 9 characters on most wire tags).

We tried to # wires similar to a PLC-5 (example: I00114 - input-rack-slot-bit) but that didn't work because we started to have duplicate #'s.  We had I/O modules in the rack with the ControlLogix PLC and also a DeviceNet rack in another panel.  We ended up with two rack 1's, two slot 1's,etc.

RE: ControlLogix Tag names & wire#'s

For the Devicenet ones could you use the node number? Or set it to a higher node so numbers don't conflict?


David Baird
mrbaird@hotmail.com
 
Sr Controls Engineer

EET degree.

Journeyman Electrician.

RE: ControlLogix Tag names & wire#'s

With the standard A-B Micro/SLC addressing in mind, what I do is create an "alias" tag for each I/O module in the rack and I give it a name that closely resembles the old micro/SLC addressing scheme.  For example, if I have a 16 point input module in slot 3, the Control Logix database will tag is as "Local:3:I.Data(.0 thru .15).  Not very helpful when writing a program or trying to assign a wire label.  I will create a new tag (DINT) with the name "I3", click on the alias box, and in the "alias for" box, you enter "Local:3:I.Data".  Now to address a point on the module, say slot 3, input 7, instead of typing "Local:3:I.Data.7", you now type "I3.7".  You can use "I3.7" as the wire tag and as a reference in your drawings.

RE: ControlLogix Tag names & wire#'s

(OP)
rdub - thanks for the example.  From an electricians perspective, many will have difficulty making the leap from "I3.7" to "Local:3:I.Data.7".

RE: ControlLogix Tag names & wire#'s

I have also used this technique with DeviceNet installations.  First assume my DeviceNet module is in slot 1.  Using RSNetworx, I assign my node 1 I/O to word 11, node 2 I/O to word 12, etc...  Again, I create an "alias" tag in the processor called "I111" and make it an alias for "Local:1:I.Data[11]".  Now when programming, all I have to use is "I111.0", "I111.1", etc...  As long as the DeviceNet installation isn't too large, this will work fine.

RE: ControlLogix Tag names & wire#'s

I just did a project with ControlLogix and our customer had us use their plant standard. Dogleg had a good point. Try this:

"Local:3:I.Data.7" would have a wire tagged as L:3:I.07


Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources