Telephone harmonic factor of generators

Telephone harmonic factor of generators

Telephone harmonic factor of generators

(OP)
Hi There

Could any one assist in replying to the following:
According to IEC 60034-1 the THF of generator must be recorded using line-to-line voltages.  The measured quantites during a test were however taken from phase-to-neutral values.  Can the formula still apply?  Unfortunately the phase angle of the harmonics were not recorded.  This way it could have been minipulated to give the correct line-to-line values.  Any suggestion on the topic will be appreciated

Thanks

RE: Telephone harmonic factor of generators

Suggestion: Comply with
Telephone influence factor (TIF): NEMA MG-1-22.43 standards
Telephone harmonic factor (THF): IEC 60034-1, B.9.2 requirements
Line-to-Line may have different harmonic content than Line-to-Neutral. It would be prudent to consider the worst case.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources