Hello all,
I am working on a project to renovate an existing freight elevator and am trying to use an existing beam (W8x13) to support a floor in the unused portion of the existing hoistway. The existing span is 11' and Mmax=5 k'. Does the metal deck we are planning to weld to the top flange (compressive flange) count for reducing the Lb to less than Lu. Thanks for any advice.
I am working on a project to renovate an existing freight elevator and am trying to use an existing beam (W8x13) to support a floor in the unused portion of the existing hoistway. The existing span is 11' and Mmax=5 k'. Does the metal deck we are planning to weld to the top flange (compressive flange) count for reducing the Lb to less than Lu. Thanks for any advice.






RE: Compressive Flange Support
You can consider the compression (top)flange as being laterally braced if the deck is properly welded to the beam (it does not need to be continously welded). Also make sure that metal decking is provided along the entire length of the compression flange.
Since the beam is part of a shaft, make sure that the metal decking does not stop short of covering the entire width of the flange. This situation often occurs in shafts and other slab openings
Are you planning to take advantage of composite action? If so, take a look at how you will weld shear studs with the metal deck.
Good luck.
RE: Compressive Flange Support
The existing beam appears to have plenty of capacity without considering the composite beam. Thanks again.