start voltage current relationship

start voltage current relationship

start voltage current relationship

(OP)
Start voltage / amprage relation ship was given to me by one of our engineers as

Arated/Ameasured = Vrated/Vmeasured
so that if you see a V drop at the motor you will also see a decrease in Ampreres.    
Is this correct????

RE: start voltage current relationship

Hi, the short answer is no. The current is dependent on the motor speed which is dependent on the load.

RE: start voltage current relationship

Pumpo:

During the starting condition yes, the voltage drop will reduce the inrush current proportional to the line voltage drop.

Under a steady HP load condition, the current will increase with a drop in voltage.

IL = HP*746/(1.73*VLL*EFF*PF)

Were
    IL = Line current under load
HP= shaft load in Horse power.
    VLL= Line to line voltage
    EFF = motor efficiency ( regularly it will drop a while with lower voltage)
    PF = motor power factor.

RE: start voltage current relationship

(OP)
could you help me with another query?
The software that we use calculates the start current from the Irms, Irms/Vrms X Vrated = Istart is that also correct if we have a correct voltage. The motor start I is estimated by the manufacturer because they do not manufacture or assemble the whole motor we do.

RE: start voltage current relationship

During start, a reduction in the starting voltage will reduce the starting current proportionally, however at full speed, this is not necessarily the case. A reduction in voltage will result in an increase in the work component of the current and at a moderate to high load, that will increase the running current.

The start current reduction is independent of load, but if the current / voltage is reduced too far, there will be insufficient torque to accellerate the load to full speed.
The start torque reduces with the squaare of the voltage or current reduction.

Best regards,

Mark Empson
http://www.lmphotonics.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources