start voltage current relationship
start voltage current relationship
(OP)
Start voltage / amprage relation ship was given to me by one of our engineers as
Arated/Ameasured = Vrated/Vmeasured
so that if you see a V drop at the motor you will also see a decrease in Ampreres.
Is this correct????
Arated/Ameasured = Vrated/Vmeasured
so that if you see a V drop at the motor you will also see a decrease in Ampreres.
Is this correct????





RE: start voltage current relationship
RE: start voltage current relationship
During the starting condition yes, the voltage drop will reduce the inrush current proportional to the line voltage drop.
Under a steady HP load condition, the current will increase with a drop in voltage.
IL = HP*746/(1.73*VLL*EFF*PF)
Were
IL = Line current under load
HP= shaft load in Horse power.
VLL= Line to line voltage
EFF = motor efficiency ( regularly it will drop a while with lower voltage)
PF = motor power factor.
RE: start voltage current relationship
The software that we use calculates the start current from the Irms, Irms/Vrms X Vrated = Istart is that also correct if we have a correct voltage. The motor start I is estimated by the manufacturer because they do not manufacture or assemble the whole motor we do.
RE: start voltage current relationship
The start current reduction is independent of load, but if the current / voltage is reduced too far, there will be insufficient torque to accellerate the load to full speed.
The start torque reduces with the squaare of the voltage or current reduction.