I have just started doing work in the US and Canada and was wondering....
In Canada CSA regulations for Switchgear Assemblies have a lower minimum spacings in air for live parts than what I see from the NEC Table 490.24 (see below).
CANADA US
2400v 2.5" P-P, 2" P-G 4.5" P-P, 3" P-G
7200v 4.0" P-P, 3" P-G 5.5" P-P, 4" P-G
13800v 6.0" P-P, 5" P-G 7.5" P-P, 5" P-G
What I want to know is "technically" who's right?? ...and don't say it depends on what country your in!
In Canada CSA regulations for Switchgear Assemblies have a lower minimum spacings in air for live parts than what I see from the NEC Table 490.24 (see below).
CANADA US
2400v 2.5" P-P, 2" P-G 4.5" P-P, 3" P-G
7200v 4.0" P-P, 3" P-G 5.5" P-P, 4" P-G
13800v 6.0" P-P, 5" P-G 7.5" P-P, 5" P-G
What I want to know is "technically" who's right?? ...and don't say it depends on what country your in!






RE: Minimum Clearance of live parts
RE: Minimum Clearance of live parts
However, that is the issue you will ultimately need to deal with, because "technically" it doesn't matter. Under the right circumstances, you could mount the components 1/8" apart and have them be just fine. However, that would be in the vacuum of space, and even then a little space dust may become problematic. The standards adopted by each authority are reflective of the conditions they deem tolerable and / or reasonable to expect. These are not "technical" absolutes, but practical ones since they will be inspected and approved by the Authority having Jurisdiction and violating THEIR rules is rarely up for discussion!
Quando Omni Flunkus Moritati
RE: Minimum Clearance of live parts
I have 2 questions with regards to your responses:
stevenal: Why do manufactured assemblies have special rules..(sounds like a dumb question, but air is air...)?
jraef: I am not quite up on my Latin (just guessing that it is Latin??)... but what does "Quando Omni Flunkus Moritati" mean??
Thanks again for your help...
RE: Minimum Clearance of live parts
The wires on my table lamp are much smaller than the circuit I plug it into also. Isn't copper copper?
RE: Minimum Clearance of live parts
RE: Minimum Clearance of live parts
RE: Minimum Clearance of live parts
"When all else fails, play dead"
Quando Omni Flunkus Moritati
RE: Minimum Clearance of live parts
The NEC is a safety standard and is concerned with clearance of people to live parts. The clearance of live parts to ground or phase-to-phase is usually not a safety concern if the parts are not accessible to people. Equipment is manufactured to ANSI standards which is concerned with the ability of the equipment to withstand voltages, either power frequency or surges.
RE: Minimum Clearance of live parts
1. Creepage distance
2. Creep distance
3. Clearances
3.a. Fence safety, IEEE std 1119-1988 withdrawn
3.b. The minimum separation between two conductors, IEEE 524-1992
3.c. The clear distance between two objects measured surface to surface, ANSI C.2-1997 NESC
etc.
Reference: IEEE Std 100-2000 Dictionary
RE: Minimum Clearance of live parts
Stevenal,
"The wires on my table lamp are much smaller than the circuit I plug it into also. Isn't copper copper?"
What am I missing??
The wires on your table lamp were sized with enough copper for an Amp or 2... the wires in your house have enough copper for 15 amps.... copper is copper...
RE: Minimum Clearance of live parts
It makes a difference if voltage peaks (and how high) are considered and imbedded in the clearance values.
NFPA 70-1999 Art. 490-24 "Minimum Space Separation" states "These values shall not apply to interior portions or exterior terminals of equipment designed, manufactured, and tested in accordance with accepted national standards."
RE: Minimum Clearance of live parts
RE: Minimum Clearance of live parts
Gotcha...thanks