Delta-Delta Transformer bank, Phase loss and Ground fault

Delta-Delta Transformer bank, Phase loss and Ground fault

Delta-Delta Transformer bank, Phase loss and Ground fault

(OP)
I have a Delta-Delta transformer bank, 13,200-480.  I would like to monitor both phase loss(ie. loss of a primary fuse) and ground fault on the secondary.
I would like to send a signal to trip a shunt trip molded case circuit breaker during a phase loss to prevent single phasing loads and alarm for a ground fault.

Any ideas.  I know I can use the Ground Detection Lights for the ground fault, but is there a relay that can handle both.

Whats the best way?

RE: Delta-Delta Transformer bank, Phase loss and Ground fault


As implied in the original post, there are two conditions that should be handled in different manners.  The problem with low-voltage ungrounded-system transient overvoltage and consequent insulation damage {often in motors} has been acknowledged in power-systems publications for 50 years.  Adaptation/retrofit to high-resistance grounding and associated  indication/annunciation is well recognized in various electrical publications.

Phase “loss” or imbalance is a bit trickier.  Voltage-imbalance detection is adequate to inhibit starting of a group of motors, but has significant limitations in protecting motors once they are running.  Unfortunately, once motors have accelerated and settle to namplate current, voltage-imbalance sensing has serious limitations, and in many cases is quite useless.  Current-imbalance protection is far more effective, but cannot reliably be applied to groups of motors.

There are a number of “ice-cube” type devices that promise to protect against electrical ills and look good in advertisements, but in terms of reliably protecting against equipment damage and production loss leave a lot to be desired.

A search in electrical topics at Eng-Tips under ‘ungrounded’/’high-resistance grounding’ and ‘phase loss’/‘phase imbalance’ will yield discussion on the matter.
  

RE: Delta-Delta Transformer bank, Phase loss and Ground fault

Suggestion to John5445 (Electrical) Jan 23, 2004 marked ///\\\
I have a Delta-Delta transformer bank, 13,200-480.  I would like to monitor both phase loss(ie. loss of a primary fuse)
///Some disconnect switch manufacturers offer the blown fuse monitor with their product as an option. E.g. see
http://www.pringle-elec.com/bolted.html
\\\
 and ground fault on the secondary.
///Modern electronic circuit breakers do have this feature available via the electronic trip unit, e.g. Square D Micrologic.\\\
I would like to send a signal to trip a shunt trip molded case circuit breaker during a phase loss to prevent single phasing loads and alarm for a ground fault.
///See the Pringle Blown Fuse Detector. It can open the switch.\\\
Any ideas.  I know I can use the Ground Detection Lights for the ground fault, but is there a relay that can handle both.
///See above comments\\\

RE: Delta-Delta Transformer bank, Phase loss and Ground fault

I'm also not aware of any single device that would do both. I have had excellent results applying the Taylor Electronics phase unbalance relay.  It's a small company that is located in Florida.  For many years they were the standard choice furnished with Square D switchboards when you ordered the phase loss/unbalance option.

For ground detection, I recommend you use the wye connected resistors approach rather than PTs.  The latter can develop ferroresonance effects under certain conditions and the resistors work just fine in a 480V application.  I'm away from the office and can't think of a brand name but there are companies who offer them in a NEMA 12 or other enclosure with audible and visual alarms and dry contacts for remote indication or tripping.   

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources