Impedance Of a Transformer

Impedance Of a Transformer

Impedance Of a Transformer

(OP)
What would be the ideal impedance for large commercial transformers (750 to 2000 kva). Is there any advantage to having lower impedance tranformers (2%)vs. (5%) transformers. I know the disadvanteges for the lower impedance tranformers are that the AIR rating of switchgear has to withstand the availbale fault current produced by lower impedance transformers. Is there a guideline for utilty companies to provide a certain impedance level so as not to force the building owner to have the expense of larger rated gear. Why do lower impedance tranformers exist?
Thanks

RE: Impedance Of a Transformer

IEC Standard for Transformer sets guideline values.

RE: Impedance Of a Transformer

Typically higher efficiency transformers have lower impedance. Some utilities purchase high efficiency transformers without consideration to the effect on customer's equipment.

5.75% is "standard" in ANSI regions, but there is a lot of variation.

RE: Impedance Of a Transformer


Lower-impedance transformers have lower copper {full-load} losses and less voltage drop with increasing load.  For ANSI regions, there are a handful of IEEE C57.12.** standards that typically apply.
  

RE: Impedance Of a Transformer

Suggestion: The lower impedance transformer has lower losses, creates smaller voltage harmonic distortion as a result of harmonic currents, causes lower voltage drops, etc. However, it causes the secondary short circuit fault levels be higher, costlier, bulkier, etc.
Generally speaking, the trend is to the higher Interrupting Rating equipment, which makes it more affordable. The advantage of such power distribution is in lower voltage drops, higher HP motors can be started with smaller voltage dips, etc. It is a matter of "pay now or pay later."
Usually, some trade offs or optimization is required. Many projects adhere to industry standards to obtain the best price for a transformer.

RE: Impedance Of a Transformer

(OP)
Are K-rated Tranformers of low impedence design?

Thank you all for your help.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources