Apply HV 60Hz CB at 50 Hz

Apply HV 60Hz CB at 50 Hz

Apply HV 60Hz CB at 50 Hz

(OP)
Ansi equipment on 50 Hz project. 4.16 KV vacuum CB's designed to previous C37 constant MVA rating, not the newer standards in the C37 series which have constant KA ratings.

Tables in the C37 standards, on preferred ratings, are at 60 Hz. Is there a procedure to use these standards for 50 Hz applications? At first glance, I imagine a slight de-rating for the increased cycle time. Also, a close examination of the basis of the C37 decrement curves seems to be warranted.

RE: Apply HV 60Hz CB at 50 Hz

I'm guessing you would have to get specific application data from the breaker manufacturer.  I don't recall the old ANSI standards having a specific de-rating for 50 Hz. It should be lower than 60 Hz.  

The newer ANSI breakers typically also have an IEC rating at 50 Hz.  But direct comparisons are difficult because test procedures and test standards are the same.  

RE: Apply HV 60Hz CB at 50 Hz

Suggestion to DPC: The test procedures and test standards are not the same in: ""The newer ANSI breakers typically also have an IEC rating at 50 Hz.  But direct comparisons are difficult because test procedures and test standards are the same.""  

RE: Apply HV 60Hz CB at 50 Hz

Suggestion: There is a trend to have the switchgear complying with ANSI and IEC standards.
The low voltage cbs are already available: Visit
http://ecatalog.squared.com/catalog/html/sections/06/17...
The high voltage switchgear are starting: Visit
http://www.abb.com/GLOBAL/ABBZH/ABBZH262.nsf/viewunid/F...$file/LTB+Compact+B4028+Ed5.pdf
http://www.ieconsult.fr/Ansi-IECComparison.pdf
http://www.siemens.fi/evu/ev/download/peg97/pegt02i.pdf
etc. for more info

RE: Apply HV 60Hz CB at 50 Hz

As Jbartos noted, I left out the "not" in the last sentence of my first post - meant to say that IEC and ANSI test standards are NOT the same.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources