HAZARDOUS AREA CLASSIFICATION

HAZARDOUS AREA CLASSIFICATION

HAZARDOUS AREA CLASSIFICATION

(OP)
GAS PIPELINE LOCATED CLOSE TO THE FENCE IS MAKING CLASSIFIED AREA - DIVISION 2 OUTSIDE OF THE PROPERTY, OUTSIDE OF THE FENCE.
AREA AROUND THE FENCE IS PROVIDED FOR THE TEMPORARY ROAD - FOR MAINTENANCE.
THE FENCE CAN NOT BE EXTENDED - BECAUSE IS NOT THE SAME PROPERTY.
HOW TO CREATE SAFE AREA? CREATING OF NO-PASSING ZONE WITH A SIGNS IS PROBABLY NOT ENOUGH ?

RE: HAZARDOUS AREA CLASSIFICATION

What is the source causing the area classification?  

Suggest you review API 500 and perhaps get an out.

RE: HAZARDOUS AREA CLASSIFICATION

Pristava: The question is; if its just a pipe you wont get any areaclassification since there are no point where gas can escape. If there are vents or other sources it might be different.

Best regards

Morten

RE: HAZARDOUS AREA CLASSIFICATION

Check the latest version of the standards as many have been revised recently. For example IP-15(2002) specified that the hazardous area round a flange on a natural gas pipe may be only 1.5m and therefore half the 3m recommended in the previous IP-15(1990) code.

RE: HAZARDOUS AREA CLASSIFICATION

jcaiken (Chemical)

Please give more detail and reference on IP-15(2002) , IP-15(1990) code.

Leonard

RE: HAZARDOUS AREA CLASSIFICATION

From memory IP-15 (1990) sized the hazardous area round flanges etc as 1.5m or 3m depending on the quality of the installation and frequence of handling. IP-15 (2002)uses a more quantified criterion based on a release size and frequency relationship and a release rate & area based on the fluid and the source pressure (up to 100 barg). For Natural Gas the maximum Zone 2 area is 1m radius but for liquid releases this could be 2.5m, or 3m if close to the ground.
I'd strongly recommend that you get hold of a copy from the Energy Institute (formerly Institute of Petroleum) as a detailed assessment based on the location of potential release sources (flanges, valves, etc.) could be the answer.
Note that a 3rd edition of IP-15 is in preparation and could be released soon.  

RE: HAZARDOUS AREA CLASSIFICATION

Pristava,
You mentioned this being a gas line (Natural Gas?).  In the US, this will probably fall under ASME B1.8 or DOT CFR 149 or both.  I would check this and follow 1969grad's advise on checking API RP500.

Chris

RE: HAZARDOUS AREA CLASSIFICATION

Okay,

So much for not being able to type. That should have been ASME B31.8

Chris

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources