GROUND PLATE INSTEAD GROUND ROD

GROUND PLATE INSTEAD GROUND ROD

GROUND PLATE INSTEAD GROUND ROD

(OP)
Communication Antenna is provided to be grounded with three
ground rods ( 3.0 m long) connected by 2/0 wires. Also connection with existing grounding is provided to be made.
Contractor is preparing to intall three ground plates instead ground rods.
Question:
How to calculate grounding in that case ? Is it possible to replace ground rod by ground plate making the same grounding resistance.
Thanks!  

RE: GROUND PLATE INSTEAD GROUND ROD

I don't have access to it here to check, but the IEEE Green Book has ground impedance calculations for many different configurations of ground equipment.

RE: GROUND PLATE INSTEAD GROUND ROD

Specify the resistance you need to the contractor then let him do the math.

RE: GROUND PLATE INSTEAD GROUND ROD

Resistance to earth can be calculated roughly if soil resistivity is known. Sometimes it is necessary to use trial and error approach (e.g. start with 2 or 3 and add more as needed to get desired result).

RE: GROUND PLATE INSTEAD GROUND ROD

Suggestion: The lightning protection should be grounded according to up to date 2000 edition of:
NFPA-780 Standard for the Installation of Lightning Protection Systems (1997)
http://www.nfpa.org/Codes/NFPA_Codes_and_Standards/List...
The antenna system grounding is specified under the transmitter/receiver spec.
See NFPA 70-2002 National Electrical Code for Article 810 Radio and Television Equipment. (There is no specific Ohms value stated for the antenna grounding.)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources