Sulfur dew point
Sulfur dew point
I am looking for a method for calculating sulfur dew point in GT exhaust gases based on H2O content in flue gases and total sulfur content in fuel.
Is anyone aware of literature on this subject?
RE: Sulfur dew point
Typically, unburnt sulfur is not one of the components.
What is your fuel?
I read this site from home in the evenings, away from my reference material. I will look in a book I have, titled "Steam" published by B&W, the boiler manufacturer, and if it is not there, I will have to scratch my head as to where I might have anything.
In general, with sulfur bearing fuels, the flue gas in steam boilers is kept above the 300-350F range to stay above the sulfur dew point. The heat transfer equipment could get it much lower, but the sulfur won't allow it.
Now, I can't tell you if that is a function of the sulfur dew point itself, per se, or a function of maintaining an air preheater outlet temperature high enough, so as to keep the "resultant" temperature of the flue gas leaving the air pre heater, which in a high percentage of cases is a Ljunstrom, and the fresh air flow from seal leakage around the Ljunstrom wheel, which is 8% guaranteed for a new Ljunstrom right out of the box, and up to 25% for units that have been in service for lots of years.
In any case, it is to keep the resulting flue gas temperature above the sulfur dew point, to prevent back end corrosion. That sulfuric acid that results when the dew point is reached is brutal.
Also, while sulfur content is taken in fuel analysis as an average, or mean value, it is well known that the sulfur can vary all over the map. If your fuel is Natural gas, you are probably not talking about much. However, if your fuel is fuel oil, check your fuel analysis samples closely.
It is one of those things that I learned a long time ago how to do, and the answer was always just stay above 300 minimum, so I did not need to calculate it any more, and, forgot how. My first GTCC was dual fuel fired, and we had to add an economizer recirc circuit to the back end of the HRSG (that was before the name HRSG was coined) to maintain the flue gas at a higher outlet temperature when firing on fuel oil, because of the sulfur in the fuel oil.
If I find something, I will repost tomorrow nite.
rmw
What B&W Steam does have, however, which I believe might be useful for you, on page 19-12 of the 40th edition, is is two figures, both of which are associated with recuperative air heaters cold end metal temperature limits, plotted against % by wt. of Sulfur in fuel. There are different plot lines for NG, Oil, and Coal, PC, and cyclone.
If you can find either of these books, I think you could use the information for what you are seeking. At this point in the process, I don't think the gasses care if they came from a GT, or a combustion boiler.
If you can't find the books, post back with some specifics as to % sulfur in the fuel, temps, and fuel types, and I will read the curves, and give you a grouping of results.
Good Luck,
rmw
Eng-Tips.com : Solving your problems before you get them.
I checked it out. That is a good site, and should answer KKanel's question. Now I have a question. Why didn't you post that before I typed in all that stuff??
I am giving you a star anyway. It is a valuable reasource.
rmw
Thanks for the undeserved star. I always enjoy your insights in other forums and my joy doubled in getting a star from experts like you.
Though I have been a member in this forum since my joining eng-tips.com, I occasionally peek in here as the activity in this forum is very dull.
PS: The owner of the website I mentioned above (Mr Jack Hardy, as I remember) is also a member of eng-tips.com and mentioned about the site couple of times here.
When I got there, I recognized that I had been there before, although on that occasion, without a particualr "quest" in mind, I did not dig in and really examine all the site had to offer. Now that I have, I see it as a really good site, and you deserve the star for bringing it to the attention, (again) of KKanel, and myself.
rmw
I have some basic curve, for dew point (ABB)now Alstom. I have to check and scan it, need some time. I believe it is for basic engineering and not detail one. your e-mail address pls.
1ton
If you put SO3 content as zero into forumula and get the water dewpoint corresponding to whatever water content you input then its a good correlation. Most do not do this.
For HRSG's burning fuel gas with 10ppm sulphur acid dewpoint is 81C, with 100ppm sulphur acid dewpoint is 93C.
Between these points interpolate on a log10 scale for sulphur and a linear scale for temperature.
athomas236
Are these two temperatures verified somehow? At 1st glance they seem a bit high!
1ton : thanks
Have checked graph and yes it is a straight line over the range mentioned with scales as linear for trmperature and log10 on ppm sulphur in gas. PPM is by volume.
Temperatures verified only in the sense that they come from an internationally renowned American GT supplier.
athomas236
