help interpretting 12-pole generator winding configuration
3
I am trying to interpret the following stator winding description for a syncronous generator stator:
KVA - 6875
Poles: 12
coils per slot: 2
Slots: 144
Connect 1 and: 4
Coils in Slot 1 and: 11
No. Circuits: 6  at 4160 Volts
Connection: 120-degrees Phase B Star: 4160
Grouping: 888 - repeated 6 times
Coils per group: 8
I know 12-poles is correct... it is a 600rpm machine (60HZ system).   If I ignore the last two items, I can piece together the following:
- we have 144/(12*3) = 4 coils per pole phase group
- Connect 1 and 4: defines pole-phase group connections for first pole phase group.
- Coils is Slot 1 and 11. Reasonable fractional pitch.  Full pole pitch would be 144/12=12 i.e. 1 and 13 .  This gives 2 coils overlap between pole-phase groups (right?).
- With 6 circuits, that must mean that each phase has 6 parallels, two pole-phase groups in each parallel.
Now the last two items throw me a curve. Why do they say 8 coils in a group?  I could understand if they said 8 coils in a circuit or parallel, but this is not normal interpretation of the word group, is it?  If not then what do they mean by 8 coils in a group?
I get to look at this machine tomorrow. Any quick reply would be appreciated. Thx.
RE: help interpretting 12-pole generator winding configuration
pete,
Since the winding has 6 parallel ckts out of 12 groups per phase, each parallel ckt in first phase has 2 groups of 4 coils each connected in series (1&4, 7&10, 13&16, 19&22 and 25&28). They probably meant coils per circuit (not group) as 8. This series grouping of two groups is repeated 6 times in each phase and 18 times in total winding covering all the 144 coils.
You are right about pitching. The coil overlap over phases is the no. of slots by which full pitch is short chorded. In this case, a pitch of 10/12 will have, in two slots (per phase per pole) coils belonging to belonging to different phases in each layer.
Thanks edison, that confirms what I was thinking.
Their use of the term "group" threw me off. I would have called this 4 coils per group, 2 groups per circuit, 6 circuits per phase.
Electricpete:
This winding is called “consequent groups” or 120°E groups. It has one half of the groups (18) as compared to a regular 60°E grouping (36). The polarity of all groups is the same. First group is phase “A”, as second group is 120°E apart, it is phase “B” and third group is phase “C”. All groups have the same polarity ( eg in +, exit  - ). Jumper is 1 – 4  to make a series with the same phase.
For 6 circuits and 18 total groups, you have one group per circuit.
Similar connection is used for two speed single winding motors in the low speed connection.
Aha. Thanks aolalde.  Great comment as usual.
I can begin to picture what you say:
Normal motor:
(ab'c a'bc')^6 = 36 groups 60 degrees apart.
36*(60/360)=6 electrical cycles per mechanical revolutions (600rpm)
coils/group = 142/36 = 4
Consequent pole motor:
(a b c)^6 = 18 groups 120 degrees apart.
18*(120/360)=6 electrical cycles per mechanical revolutions (600rpm)
coils/group = 142/18 = 8
Jumper 1-4 means same polarity of groups 1 and 4.
How would normal motor pole jumper be identified?
Jumper 1-4'?
Also, why would a designer choose consequent pole winding?  (for one speed machine)
aolalde,
As pete says, I do not see any reason to use consequent pole winding in single speed machine and that too in generators, where harmonics will be a big problem when consequent pole winding is used. As you say, it is typically used in single winding two speed low voltage motors.
Also, a 120 deg phase band does not mean automatically consequent pole winding. It defines only the phase spread of the winding and not the pole to pole connections.
Again a more common 60 deg phase spread gives about 15% more fundamental distribution factor (0.955/0.827) as compared to a 120 deg phase spread. Since this gives a 15% more output for a given current, a 60 deg spread is preferrred by winding designers.
pete,
You mentioned about that you will get to look at the actual winding. May be you can post here what sort of winding is actually there.
Hi; Electricpete & Edison123.
I’ll wish to answer your questions but I never designed a Generator winding this fashion, I have found a few (2 on Electric Products Generators with this winding).
What I found is that connecting the winding is simplified since the amount of jumpers is reduced. If the question about 1 – 4 jumper as  compared to length for standard  60°Grouping, the length of the phase coils terminal lead is like that for a std 1 – 7 jumper coil. For this winding the simplification is great since all your groups are lines or neutral (4, 5&6) for 6 circuits. Probably this winding has six terminal leads (1 to 6) around the winding with six connection points to each lead and no jumpers.
Edison, remember that at a given instant, the fem induced on each conductor has amplitude and angle related to the position (slot) it keeps between each North and South Pole, then when connected in series with other conductors the resultant voltage will be the vectorial addition of all the fems in the series conductors. That is true for the fundamental and any harmonic. The designer should optimize the resultant voltage for the Fundamental and minimize total voltage result for harmonics. I think that this winding eliminates totally the 3rd harmonic (I have read that wye connection does too, in regular windings). You could try to find a distribution factor by the books and rules or better, make the analysis of this particular array. There are some few generators outside with non conventional windings.
My thought, like edison, is that this design would produce higher space harmonics.
aolalde has correctly decuded this is in fact an Electric Products Generator.  Based on that and his other comments, something tells me he knows a lot more about electric machines than me.
We will be rewedging this generator and I will have a change to take a look at the connections.
aolalde,
Pete posted that this m/c has 6 circuits and also "connect 1 & 4". If it had been a consequent pole winding, then question of connecting 1 & 4 does not arise since all 8 coils are serially connected to produce N (or S) poles.
So, my bet would still be it is a normal pole connected winding with 60 deg phase spread with 6 jumpers/phase and with 36 pole-phase groups having 4 coils each. May be pete will be kind enough to post his findings.
Reg, your last paragraph, while I agree what you've said, I still don't undertsand what you are really trying to say. If you disgaree with my earlier post, I will be glad to correct myself.
Edison
Please analyze my comments to your post:
"I do not see any reason to use consequent pole winding in single speed machine and that too in generators, where harmonics will be a big problem when consequent pole winding is used”.
I calculated the distribution factor for the fundamental and harmonics up to the 13TH with the following results:
        1st        3rd        5th        7th        11th      13th
60°    0.9577    0.653    0.205    0.1575    0.126    0.126
120°    0.8294    0.0    0.1778    0.1365    0.1091    0.1091
Kp    0.9239    0.3827    0.3827    0.9239    0.3827    0.3827
All the low range harmonics will be reduced with actual winding, as compared to the conventional 60°E group belt.
I think this winding has a premium performance regarding the 3rd harmonic for line to neutral loads. It is totally eliminated.
 “Also, a 120 deg phase band does not mean automatically consequent pole winding. It defines only the phase spread of the winding and not the pole to pole connections.”
 If the electrical spacing of each group of coils is 120°E, the fourth group has 360 °E out of phase, is not this consequent? The salient poles polarity is still N,S,N,S, etc
and should have 12.
I agree that  for the same current the power output could be up to 15.5% higher with a conventional 36 groups winding as the fundamental voltage increases, but that should be considered at the original design evaluation, the output against quality of the generated wave. My best advice is leaving it with the original design (if it is as I assumed).
Thanks both of you for your interest.
aolalde,
I have worked distibution factors for various harmonics as below. (correct me if I am wrong)
Spread       1st      3rd        5th           7th         9th harmonic
60°         0.955    0.637    0.191    - 0.136        -0.212
120°       0.827    0.0       -0.165      0.118         0.0
With a star connection, the 3rd harmonic is eliminated across line terminals and with 5/6th chording used here, the spread factors for 5th and 7th are reduced to 0.259, which gives a reasonably clean waveform with a 60 deg spread. (Unless there is a line to neutral circuit in use that requires a very clean waveform, which pete can confirm).
Why I am puzzled in this case is that "connect 1 & 4" which does not arise in a 6 ckt in a 120 deg spread.
As you rightly said that the phase spread advantage is taken care of in the design stage, which is exactly why a designer would choose a 60 deg spread to avail the increased output benefit which results in a smaller machine.
Anyway, thx for making this thread interesting. Rest is now in pete's court.
Comment on electricpete (Electrical) Jan 19, 2004 marked ///\\\
///Windig described by words only without winding figures to follow often leave some ambiguities.\\\
KVA - 6875
Poles: 12
///implies 6 pole-pairs\\\
coils per slot: 2
///1 side of two coils\\\
Slots: 144
///144 slots / 2 coils per slot = 72 coils per pole pair
72 coils per pole pair / 12 poles = 6 pole pairs
Connect 1 and: 4
/// 8 in 8 slots + 8 in the next appropriate 8 slots + 8 in the next appropriate 8 slots gives 24 slots. Repeated 6 times give 6 x 24 = 144 slots.\\\
Coils per group: 8
///8 coils per 8 slots. This gives 144 coils occupying 144 slots.\\\
///Agree\\\
///There are 144 slots and 144 coils\\\
///6 circuit x 6 parallels x 2 group = 72 slots instead of 144 slots.\\\
///To cover one phase. Notice 888 taken 6 times.\\\
///See above\\\
Thx kumar (edison) and aolalde.
I spent awhile studying pitch and distribution factors last night and still have some more studying to do.
I can see right off the bat that the pitch factor is unchanged as aolalde says.
The distribution factor as I understand it describes behavior of harmonics for a single pole-phase group.
Now there remains the question of adding the effects of the groups together.  The harmonics of the sum (as fraction of fundamental) cannot be any higher, but it can be lower if there is full or partial cancellation of harmonics among groups. For example triplen harmonics as edison said are completely cancelled.  Although I can't prove it my intuition tells me that there is better cancellation of harmonics when we add the 60-degree groups together than when we add the 120 degree groups together.
Here is some unscientific reasoning that leads me to suspect the 120 degree winding has higher content of low-order harmonics (5,7,11,13).  Let's say had a single-layer full-pitch winding with very very large number of slots so that the steps of stator slotting become negligible... instead within a group the mmf distribution curve looks like a straight line.   The mmf of that winding for 60-degree winding at given snapshot in time will look like a sin-wave constructed out of 6 straight straight lines (over one period of fundamental... two pole pitches).  In contrast, the mmf of that winding for 120 degree winding will look like sin wave constructed out of 3 straight lines over the same fundamental distance.  Clearly much higher harmonics for the 120-degree winding in that case.
Edison123
How did you calculated the distribution factor?
Distribution factor is defined as:
Kd = (magnitude of resultant voltage)/(sum of magnitudes of individual coil voltages)
after some  algebraic simplification;
Kd= sin(q*a/2) / (q*sin(a/2))
Were    q = number of slots per group
    a= slot pitch angle in electric degrees
For this generator fundamental frequency:
            q=8
a=360*6 (pair of poles)/144 (slots) = 15°E
Kd= sin(8*7.5)/(8*sin7.5)=0.8660254/1.044209
Kd= 0.829359787  is’nt it?
you got Kd= 0.827 ¿?
if q=4
Kd= sin(4*7.5)/(4*sin7.5) = 0.957662197
you got Kd=0.955 ¿? and so on.
aolalde,
I have reworked distibution factors for various harmonics as below. Sorry about that.
60°         0.958    0.653    0.205    - 0.158        -0.271
120°       0.837    0.0       -0.224      0.224         0.0
Electricpete I do not agree with your last statement:
“The harmonics of the sum (as fraction of fundamental) cannot be any higher, but it can be lower if there is full or partial cancellation of harmonics among groups.”
The harmonics cancellation in each group is given by the distribution factor and the  pitch factor Kd*Kp for each frequency.
For example for the 5th
60° group --- Kp*Kd = 0.205*0.3827 = 0.07845, this induced harmonic is reduced to 7.84%
120° group --- Kp*Kd = 0.1778*0.3827 = 0.068044, this induced harmonic is reduced to 6.8%
The harmonics that remain in a group cannot be reduced with the connection of the groups except for the 3rd in a wye connection and only from line to line.
For 60°E or 120°E groups, the next groups have identical harmonic content and out of phase in whole multiples of 360°E, then there is no possible elimination.
As I mentioned the 3rd harmonic with 60°E groups  is the exception since 3* 60°E = 180 °E so if two adjacent groups are connected together, the 3rd harmonic content of that group cancels that in the first group because is identical in magnitude and with reversed polarity ( 180°E offset) .
Clarification: 2 coils per slot also lead to a double layer machine. Double layer windings usually lead to simpler end connections, and to a machine which is more economical to manufacture. These machines are found in all machines except some small motors below 10kW.
I agree as aolalde has pointed out I was wrong: there is not cancellation among 5, 7, 11, 13 etc space harmonics of different groups.  Rather, these space harmonics 5,7,11,13  all in-phase among groups.  Thanks very much for identifying that misconception to me. I didn’t believe it until I worked it out (below).
One thing I disagree on the minor point  that the non-existence of 3rd space harmonics of mmf is dependent on the connection wye or delta.  As shown in the same analysis below, the 3rd space harmonics among adjacent groups are a total phase difference of 240, therefore any group of three will sum to zero. I understand that 3rd time harmonic currents (a different type of harmonic) are zero-sequence and cannot flow in ungrounded wye winding. That is a slightly different subject.
Here is my discussion.
The mmf space harmonics are given by   Ak*cos(w*t + k * theta*p/2  + Phi_k)
Where
w = 2*Pi*Fline
p’ = number of pole pairs  = 2*p (=6 for our example).
theta = mechanical angle
k = order of mmf the space harmonic of interest
k<0 means reverse rotation
(k = 1 = main/working p-pole mmf wave )
Ak = magnitude of the kth space harmonic
Phi_k = phase angle of the kth space harmonic
N (below) is index for counting groups.
Assume we have a normal 60-degree spread machine (not consequent pole).
D1 = “Wavelength” of the main (working) mmf is 360 / (p/2) = 720/p DegreesMechanical
(I apologize for terminology – “wavelength” here is intended to mean twice pole pitch, the spatial analogy of  to “period” for time variation).
Dk = “Wavelength” of the kth space harmonic = Wavelenth of main mmf / k = 720/(p*k) DegMech
PP = Pole Pitch = Wavelendth/2 = 360/p DegMech
Dpg = Spatial Distance between adjacent pole-phase groups = PolePitch / 3 = 120 / P DegreesMechanical.
Dpgk = Spatial Distance between adjacent pole-phase groups expressed relative to wavelength of kth harmonic =  Dpg/Dk   = [120/p] / [720/(p*k)] = k/6 = k*360/6 = k*60 degrees expressed on kth spatial harmonic basis
DeltaT = Time difference between adjacent groups = 60 degrees.
Total angle difference between adjacent groups for kth harmonic is Dpgk+DeltaT = 60+k*60 = (K+1)*60
For k=3, the pole phase groups are separated by (3+1)*60 = 240 degrees.
These are equal magnitude but angle separated 240 degrees => any adjacent group of 3 cancel out.
For k=5, the pole phase groups are separated by (5+1)*60 = 360
All in-phase as aolalde has said.
For k= -7: the pole phase groups are separated by (-7+1)*60 = 0, -360, -720 etc.
Now I have some questions on the big picture of kd and kp for the harmnonics.
Do you agree:
We use kd and kp to predict the magnitude of stator space mmf harmonics (in presence of stator slotting), and that magnitude (relative to fundamental) is given by (kd*kp / nu) where nu is the order of the harmonic?
- The same numerical kd and kp are also used to predict voltage (and exciation current) harmonics arising from non-sinusoidal air-gap mmf.   This would not include mmf harmonics caused by stator slotting itself (these occur in standing wave forward/reverse paris and therefore  are stationary with respect to stator coils), and so would be limited to harmonics associated with the rotor or eccentricity.  There is no factor nu (space order) here as was used above.
What are other uses of kd and kp (other than relating fundamental voltage to flux, turns etc).
Electripete.
Congratulations, you have made a great homework.
I have one last comment that I hope will help to center your thoughts.
If the magnetic flux distribution in the air-gap produced by the field poles were following a perfect sinus distribution and no distortion due to slots, saturation etc should exist; then you will induce a perfect fundamental voltage in the stator winding. (No harmonics).
As this ideal condition will not exist, the harmonic voltage induced will be proportional to the type of distortion on each particular generator.
A properly designed winding will get rid or at least will reduce to a minimum the remaining harmonic voltage induced. This could be achieved with the coil span, grouping, skewing, etc.
I made a comment "This would not include mmf harmonics caused by stator slotting itself".  I think you have expressed disagreement.
Here is why I said it.
Energize the stator with 3-phase sinusoidal 60hz.  Neglect saturation.  Lock the rotor to prevent movement.
I believe the current which results must be purely sinusoidal.  Why shouldn't it be?  We now have a pure linear system.  The phase voltages are the inputs (independent variables). The outputs (dependent variables) are fluxes and currents... these are all determined by linear operations (addition, scalar multiplication, differentian integration), and the system characteristics are not time varying.  Is it agreed?
So, we have slotting, but no harmonics.  My contention is that stator slotting does not cause stator current harmonics.
One more question. I have just built a spreadsheet for kd and kp. I tested results for the machine described in this post except assuming 60 degree spread.
I got results which agreed except for kp.  I get the following values for kp
1.000    3.000    5.000    7.000    9.000    11.000
0.924    -0.383    -0.383    0.924    -0.924    0.383
Never mind my post on kp.  I think it agrees if use coil pitch =9. Should use coil pitch=10.
I had a winder look at our generator. I asked him to explain the windings (I didn't give him any hints). He said it must be a consequent pole machine.  Aolalde was 100% correct.
An interesting thing, we have 18 groups of 8. Each of those groups of 8 has both leads brough outside the machine.  (36 leads attaching various points all leave the machine).  The only jumpers within the machine are the series jumpers. All other interpole connections must be made external to the machine. (I don't have opportunity to look at that part of the equipment yet).
Why would they do it like that?
pete,
You mentioned in your first post "connect 1 & 4". Was there such a connection between first and fourth group ? If not, then aolalde was correct.
In a 6 parallel, 120 deg spread winding like yours, all the six starts (six pole-phase groups) of one phase will go to the line terminal of that phase and all the six ends will go the neutral. It is repeated for other two phases.
Epete & Edison123:
Please read my first post of this thread ( Jan 23) about grouping.
1-4 jumper is only a generic information that could apply if more than one group per circuit is required.
Jumper 1 and 4 could apply equally to consequent pole or normal motor, correct? (the difference being top-to-top or bottom to bottom jumper for normal, and top-to-bottom or bottom-to-top for consequent pole).
I have inspected the stator in the shop.  There are as the drawing says 18 groups of 8 coils in this 12 pole motor.
There is not a single jumper connecting any of the groups in the end-winding area.  Every single one of those 18 groups has two leads brought outside of the machine through a melamine block.  Quite a collection of leads circling the connection end and 36 total leads leaving the generator.
I have not had an opportunity to inspect the external device where the connections must be made.
Do you have any idea why would they bring all those leads out instead of making connections in the machine?
pete,
Thx for clearing that "connect 1 to 4" mystery. While it can apply to consequent pole or normal winding, in your case given the no. of parallel ckts, that would not have been possible. All my posts about normal winding were based on this particular (mis)information.
As far the taking out all the parallel leads outside the m/c, the following are the reasons.
1. To have all the six ckts of one phase (which are distributed around the m/c periphery)in parallel would require minimum of 3 rings (for three phase leads) and 1 ring for (neutral leads)and maximum of 6 rings (i.e. 3 neutral rings) if you need differential protection. Again from these pole connecting rings, you have to run heavy cables to the terminals to carry the entire stator current. So, it is lot easier to take the pole-phase leads (which have to carry only 1/6th current and hence lot smaller in size) themselves outside the m/c, where they can be paralleled comfortably without being constrained by the machine diameter. I personally would have this arrangement only for it makes the winding inside the bore less cluttered and more easy to work with.
2. By having all the six ckts brought outside, one can test any of these individual pole-phase groups (for hipot, surge, IR, etc.) easily anytime in future and get comparative and better test results.
3. If you are keen on an elaborate differential protection, one can protect each parallel ckt, which is more sensitive to turn faults etc., than having just one CT on each end of bunched phase and neutral leads.
btw, I have worked out the harmonics for your winding for both 60 deg spread and 120 deg spread and found that other than 3rd harmonic components (which are eliminated across lines anyway), the 60 deg spread has lesser harmonics than the 120 deg spread. If you are interested, you can mail your id to eewemf@yahoo.com for my reply mail.
Anyway, I enjoyed this thread very much, thx to you and aolalde.
Kumar
Comment on electricpete (Electrical) Jan 28, 2004 marked ///\\\
///The symmetrical components are resolving the fundamental waves into positive, negative and zero sequence components. The harmonics can also be resolved into positive, negative and zero sequence components. The delta winding will trap triplen harmonics. It passes non-triplen harmonics; however, no zero sequence components, fundamental or harmonics. Essentially, the zero sequence components are essentially propagated over the ground paths. The delta winding does not have any connection to the ground.\\\
Question to electricpete (Electrical) Jan 28, 2004
Please, may I have the following clarified?
""harmonic =  Dpg/Dk   = [120/p] / [720/(p*k)] = k/6 = k*360/6 = k*60 degrees expressed on kth spatial harmonic basis""