Hi
  We have four energy saving devices (Atto power misers) fitted to 75kw motors, we have two mcc's fitted with two power misers each, If one of the powermisers has the mccb switched off then back on whilst the other powermiser in the same panel is till running that powermiser shuts down, a similar effect happens when the powermiser starts up. All control cables running to the powermiser are screened and run seperatley from or where not practical to run seperatley at 90 to power cables.  

RE: three phase motor energy saver

Hi, put suppressors on your contactor coils (VDR or RC or both).

RE: three phase motor energy saver

Suggestion: Visit
http://www.powermiser.co.uk/
for Virtual Powermiser
Apparently, it may be a good idea to simulate the PowerMiser applications first.

RE: three phase motor energy saver

(OP)
the power misers are all solid state and have no contacors fitted.

RE: three phase motor energy saver

Clarke,

Sounds like one of the units is being affected by voltage fluctuation when the other is switched. How stiff is your supply? 75kW is a fair load to switch, especially if it is in an MCC located some distance from the distribution transformer. Is this problem an HVAC system with a roof-mounted plantroom by any chance?

Suggest you get a 'scope with an isolation probe (or an insulated scope) and see what happens to your local supply voltage as you switch the drive on or off.

RE: three phase motor energy saver

Suggestion: Powermiser tech support would be appropriate for assistance during troubleshooting.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources