Reinforcing a Field Modified Precast Lintel
Contractor installed the garage door lintel 3" too low and now has to remove the bottom 3" of the header beam. Current header is a 32" deep x 8" wide masonry header with a ublock on top with a #5 and a 8" hollow pre-cast lintel with a #5 in the bottom. The whole thing is grouted solid. Since the 3" to be removed includes the bottom #5 rebar, our only options are to reinforce the bottom of the header. Building has been dry-walled and stuccoed and is awaiting CO. Uniform unfactored load on the beam (including self-weight) is 680 PLF over 16' opening.
Unfortunately this situation happens regularly so we are trying to formulate a list of fixes based on economics and loading.
Options being considered are to reinforce with a:
1. Steel flitch plate on the inside only. Plate to take entire moment (21.8 k-ft).
2. PT LVL of LVL with felt between masonry & wood. LVL to take entire moment.
3. Double steel angles (one each side) along bottom of the beam. Design as composite concrete-steel.
4. What you got?
We are also considering other options such as personnel elimination (with extreme prejudice) when this reoccurs with the same super/shell contractor.
4. What you got?
I just hang here (occasionally)
RE: Reinforcing a Field Modified Precast Lintel
Both the special mortar and epoxy are likely to successfully sustain the whole of the required shear transfer forces.