Slip Critical Connections
2

Slip Critical Connections

Slip Critical Connections

(OP)
What are the torque requirements for a 3/4" Dia A325 bolt in a slip critical connection.  Where in ASD manual do you find it?

RE: Slip Critical Connections

You should be seeking the required tension and not a torque value. Table 4 of the ASTM A325 or A490 Bolts has the information you are looking for in the back of the AISC - ASD, 9th edition. Table 5 will give you the turn of the nut minimum rotational values.

RE: Slip Critical Connections

CWIC is absolutely correct. You need to tension the bolt to the required tension. I recommend that you require the erector to you load indicating washers of some DTIs (direct tension indicators).

Visit the following site http://www.appliedbolting.com

They have great deal of information on DTIs.

Good luck

RE: Slip Critical Connections

You might want to consider the use of TC (Tension Control) bolts. They have a spline that twists off at the required torque.

RE: Slip Critical Connections

TC bolts are the way to go.  I haven't seen a DTI in about 7-8 years.  They are clumsy to use.......You need the gage.  

Most if not all the erectors in my area (NE-CT) use TC bolts.  Even if the SER does not specify them.  

Regardless of what bolt type you use.  The most critical ( little joke there) is that the bolts be properly tightened.  The erector should first snug-up all the bolts to bring the steel (connection angle and beam web) into contact before fully tensioning the bolts.  If the bolts are not first "snugged-up", you will have relaxation of the bolts in which they appear to be fully tightened but in reality are loose.  

RE: Slip Critical Connections

Getting back to your question about bolt torque, the erector should calibrate impact wrenches on site to correlate the torque with the required tension.  This should be done with each wrench at least once a day.  Similarily the steel inspector should calibrate his torque wrench in the same manner if using torque to check the tightness of bolts.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources