transformer replacement, different power rating
For replacing transformers with spares of same voltage ratio but different kVA rating, what do I need to consider for replacing on the same protection network, ie which side do I need to construct fault currents for and how?
RE: transformer replacement, different power rating
A change in fault current requires checking he capability of the c.t.'s supplying the relays. The CTs must (1)supply enough secondary amps to permit pickup, and(2) not saturate during a fault. Lower kVA ratings will affect (1); higher kVA ratings will affect (2). In addition the fault level on the secondary must be calculated to see that the switchgear can interrupt the fault.
As recommended by "njengr1", you shoud consider and check the CT ratio of primary and secondary side of transformers and protective relay settings.
I agree with jghirst, adding 2Mva could bring the switchgear out of spec. and become a danger.
regards,
Danny
You need to check your CT knee voltage, ratio and burden. with the new short cir. current.
New transformer approximate short circuit current level on its secondary is:
Isec=6000kVA/(sqr3 x 3.3kV) ~ 1050Amps
Isec,sc=(1.0/0.068) x 1050 ~ 15441Amps
Old transformer approximate short circuit current level on its secondary is:
Isec=4000kVA/(sqr3 x 3.3kV) ~ 700Amps
Isec,sc=(1.0/0.069) x 700 ~ 10145Amps
and
6000kVA/4000kVA=1.5 ~ 1050Amps/700Amps ~ 15441Amps/10145Amps
I think my posting could make you confused.