Purlins rotated at 20 degrees

Purlins rotated at 20 degrees

Purlins rotated at 20 degrees

(OP)
I have been doing engineering for timber construction for three years and have forgotten some of the particulars of designing with steel.  I even wrote a spreadsheet that does what I'm about to ask, but I want to verify for the final time that I am looking at it correctly.

I have purlins that are spanning about 20 feet and are rotated about the centroidal axis about 20 degrees (4:12 pitch).  I have metal deck between the purlins.  I believe it is prudent to resolve the vertical DL + LL into strong and weak axis bending.  This seriously changes the size of the member.

I assume the deck braces the member, as well as, prohibits any secondary effects such as torsion due to eccentricity.

Am I missing something or am I correct?

Thanks.

RE: Purlins rotated at 20 degrees

Resolving the vertical loading into strong and weak axis components is one valid approach.

Another approach that can be more economical is to design the individual purlins for the strong axis component only and to utilize the diaphragm to resist the weak axis component.  The diaphragm is designed as a deep beam with the purlins at the edges designed to be the chord members and resisting axial loads.

RE: Purlins rotated at 20 degrees

If the purlins are Z shapes, then you will still have a rotational force (between supports). This is due to your strong axis component being applied to the Z flange, which has an eccentricity about the centroidal axis of the Z.  Bottom flange bracing combined with the top flange bracing will resist this torsion in the form of a couple.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources