Hello,

I am trying to spec out an Automatic capacitor bank for the first time.  The cap will sit on the 600v side of 100kva 2400v/600v transformer along with a couple motor loads. No drives, or plcs are present so I have been told that harmonics are not a problem.  The rating of the capacitor we have chosen for the system is a 600v,300kvar,60hz capacitor bank.  However, I am not sure about other ratings such as kvar/step and step sequence, etc? Anythoughts?

Thanks in advance.

RE: Automatic Capacitor Bank

Suggestion: It may be prudent to contact the specified product manufacturer for details. In some instances, the manufacturers have general specifications that are just required to be customized.
Visit
http://www.electrotekltd.com/products/highman_products....
or equivalent,
for more info

RE: Automatic Capacitor Bank

tulum, a 300kVAR capacitor for a 100kVA transformer? Or did you mean 1000kVA?
As for the size of the steps, three to eight can be typical, and this would depend on the range of PF you are trying to correct. You want the size of the steps to be small enough so that you will not cause overcorrection.
The newer units automatically randomize the sequence of switching so that each step is used equally.

RE: Automatic Capacitor Bank

(OP)
Dandel,

Thank you... you are right 1000kva.

RE: Automatic Capacitor Bank


For low-voltage capacitors, I am not a fan of ‘midget’ {Class-CC, -T, or type-M dimension} fuses for capacitor-can overcurrent protection—Class-J fuses are consistently more “durable”.
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources