Hi all,

I am wondering for a generator of fixed rating, does an induction generator or synchronous generator have better fault ride through capability.

I imagine it would rely quite heavily on the inertia of the rotor.  So which topology has a the highest inertia rotor.  Also a synch genny will rotate slightly slower.

I guess this leads onto another question, for equal rating will a synch generator or induction generator be heavier/bigger.  I would guess a synch generator would be smaller as I imagine the airgap flux density would be larger than that of an induction generator due to excitation rather than induction (all things being equal).

RE: Fault ride through capability

Suggestion: Normally, it is prudent to trip a generator on the fault. Is this a theoretical question? When it comes to a heavy load transient, then it would depend on the rotating mass inertia.

RE: Fault ride through capability

I'm not clear what you mean by "fault ride-through" as applied to a generator.  

RE: Fault ride through capability

(OP)
When I say fault ride through I mean the ability of a sync generator to remain in synchronism with the grid when there is a network fault that is cleared.

Refering to the swing equations it seems that rotor inertia is the main factor.  Assuming this is true which topology would have a rotor of greater inertia.

What I don't understand and have't been able to find any literature on is fault ride through (or the equivalent of) for an induction generator.  I realise there isn't a syncronisation issue but there must be the concern of motoring/reverse power or large current transients or reactive power issues?

RE: Fault ride through capability

I don't think loss-of-synch is generally a problem for synch machines during a fault.  The concern is heating due to high current demand.  

For an induction generator, you will generally lose your excitation since the bus voltage will go near zero, so I would not expect them to help you much.  If you tried to keep them on line, the speed may go high.  

But I'm not burdened by a lot of actual knowledge about induction machines, so it's easy to speculate.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources